Previous in Forum: airconditioning question   Next in Forum: Unit conversion of "Thermal Conductivity" & "Specific Heat Capacity"
pressure in inlet flare's tip
09/08/2008 12:13 AM
Hi(Urgent)
please tell me the max.inlet pressure flare's tip(sonic);
Or in equation mach No. and pressure in API 521 what is the max.Pressure?
Thank you
Re: pressure in inlet flare's tip
09/08/2008 12:53 AM
As per API 521:
Mach = 1.702x10-5[W/(P·D)][ZT/(kMw)]0.5
Where:
Mach = Mach number
W= gas flow rate in pounds per hour
D = tip inside diameter in feet
P = tip out pressure in pounds per square inch absolute
Z = gas compressibility factor
T = absolute temperature in degrees Rankine
Mw = gas molecular weight
k = ratio of specific heats (Cp/Cv)
One may want to permit a velocity of up to 0.5 Mach for a peak, short-term, infrequent flow, with 0.2 Mach maintained for the more normal and possibly more frequent conditions for low pressure flares
09/08/2008 1:43 AM
Thank you for your attention
I don't understand you say that the P is atmospheric for sonic tip(high pressure)?
can i use the pressure of inlet fluid is 100 psig.and is this pressure effected in P(in equation)?
Mach no:0.65
Regards,
08/23/2011 12:12 PM
in API RP 521 not any recommendation about sonic flare.
i think it can mach : 0.8 approxmately because in sonic flare energy is need for flareless operation
best regards