Anonymous Poster

Selection of Lightning Arrestor for outdoor switchyard

09/10/2008 12:06 AM

How to select Lightning Arrestor for outdoor HT switchyard? Normally, the voltage rating of Lighting Arrestor is less than the system voltage. why?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#1

Re: Selection of Lightning Arrestor for outdoor switchyard

09/10/2008 10:10 AM

Because surge arrester ratings are maximum phase to ground voltages based on the required protective levels or margins.

Reply
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#2
In reply to #1

Re: Selection of Lightning Arrestor for outdoor switchyard

09/11/2008 12:29 AM

For a 66kV system we provide a lightning arrestor with a rating of 60kV. This does not match with the value of phase to ground voltage. Please throw some more light.

__________________
Atlas Shrugged - JGD
Reply
Active Contributor

Join Date: Mar 2008
Posts: 10
#3
In reply to #2

Re: Selection of Lightning Arrestor for outdoor switchyard

09/11/2008 4:19 AM

It is taken as ~ 80% of the highest system voltage.

Reply
Anonymous Poster
#4
In reply to #3

Re: Selection of Lightning Arrestor for outdoor switchyard

05/15/2009 4:13 AM

"The selection is done at 80% of highest voltage", this statement is wrong.For 400 KV system we can select either 360 KV or 390 KV. It depends on the insulation co ordination study.

Reply
Anonymous Poster
#5

Re: Selection of Lightning Arrestor for outdoor switchyard

07/17/2010 1:13 AM

1.5 times of Phase to Earth Voltage. (i.e) System Voltage/root 3 x 1.5

Reply
Power-User

Join Date: Feb 2011
Location: Shimurali, Westbengal,India
Posts: 119
#6
In reply to #5

Re: Selection of Lightning Arrestor for outdoor switchyard

02/23/2011 6:45 AM

Lightning arrester name plate voltage rating depends upon the following calculation-

for 400kv nominal system voltage, the maximum system voltage may be 420KV. Then peak voltage 420x1.414=593.88= 594(approx)

then phase to ground voltage = 594/1.732 = 343 (approx).

for gap-less type ZnO arrester,there are some definite standard ratings depending upon the material of LA. therefore we hve to choose the LA voltage which is equal or greater than 343KV. since 390KV is the standard rating just after 343KV, therefore you have to select 390KV rating arrester in your 400KV ss.

Reply