The NGR value of a 11KV 8.5 MW generator is 1270 ohm. How to derive the above resitance value or what is the procedure and can we find charging current from the above value. Kindly please clarify.
I think he means NGR's charging current during normal operation. It is dependant of the system capacitance to the ground and thus must be calculated (there are also some tables ready for this).
The above 5A is not the charging current but the resistive fault current. More NGR stuff in linky: