Generator NGR resistance

09/11/2008 4:02 AM

Dear sir,

The NGR value of a 11KV 8.5 MW generator is 1270 ohm. How to derive the above resitance value or what is the procedure and can we find charging current from the above value. Kindly please clarify.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Generator NGR resistance

09/11/2008 8:57 AM

I=11000/(1.73 X 1250)= 5 A ,

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Generator NGR resistance

09/11/2008 3:39 PM

What to you mean by derive (do you mean how to size a NGR for an application)? It's a neutral grounding resistor.

Neutral grounding resistors don't "charge". Do you actually know what a neutral grounding resistor is and why it is used?

Could you explain you question more thoroughly please.

__________________
jack of all trades
Reply
Active Contributor

Join Date: Jul 2008
Location: Finland
Posts: 22
#3

Re: Generator NGR resistance

09/12/2008 1:09 AM

I think he means NGR's charging current during normal operation. It is dependant of the system capacitance to the ground and thus must be calculated (there are also some tables ready for this).

The above 5A is not the charging current but the resistive fault current. More NGR stuff in linky:

http://www.startco.ca/library/papers/PowerTestPaper.pdf