3 pole or 4 pole or TPN ACB (Air circuit breaker)

09/14/2008 2:50 AM

Dear friends,

In our plant, it was decided to use old LT panels (PCC-power control center) in the new (proposed) substation. This decision saves us cost and time. But the old LT panels have 3P Air circuit breakers (L & T Make), while the SLD prepared by the consultant shows 4P Air circuit breakers.

My question is:

Can we go ahead with the 3-Pole ACBs ? Please note that all over the plant 4 pole breakers are being used. what are the practical/technical problems that may arise during operation ? How does 4 Pole ACB compare with that of TPN (Three pole - Neutral )

Please clarify

Regards

Prashanth

India

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: 3 pole or 4 pole or TPN ACB (Air circuit breaker)

09/14/2008 11:41 AM

Without having the single line drawing in front of us and without knowing the scheme used for establishing, if any, the ground system in use in your facility, any answer given to you would be not much more then a guess nor not much better then one either.

Whether or not the neutral is to be switched depends upon many factors. Best advice... talk this over with your consultant. You need to KNOW all the ramifications of this decision before you make it.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Associate

Join Date: Jun 2007
Location: dubai,UAE
Posts: 43
Good Answers: 1
#2

Re: 3 pole or 4 pole or TPN ACB (Air circuit breaker)

09/14/2008 1:06 PM

Can you provide sufficient details like How many incomers are feeding(any parallel operation)? Neutral Ratings of ACB

__________________
dennis
Reply
Anonymous Poster
#3

Re: 3 pole or 4 pole or TPN ACB (Air circuit breaker)

09/15/2008 3:22 AM

Pls note that your terminology says that its a PCC (power control center),means that you may have 3ph motive or industrial load and single phase lighting loads and other small loads which requires phase and nuetral.In this case a 4P is mandatory but instead you will be only using to power three phase loadss like motors means your 3p breakers would be adequate.

In addition to this if you are more interested to only utilise 3p breakers and in the field you can provide a D/Y transformer to avail nuetral according to your load requirements,this will save lot of copper which avoids 4Runs of cable,

But at the same time pls be carefull that the panel should be having only one source of supply.

for further querries pls dont hesitate.

Reply
Associate

Join Date: Sep 2008
Posts: 39
Good Answers: 1
#5
In reply to #3

Re: 3 pole or 4 pole or TPN ACB (Air circuit breaker)

09/16/2008 1:08 PM

Dear Guest,

Thank you for taking time to put-forth your comments. The panels are fed from two different sources of supply with an interlock between the two.

Also i would like to know the difference between 4P and TPN

Regards

Prashanth

India

Reply
Participant

Join Date: Mar 2009
Posts: 2
#7
In reply to #5

Re: 3 pole or 4 pole or TPN ACB (Air circuit breaker)

04/04/2009 11:35 AM

Dear friend,

Pls note that in 4P breakers neutral is opened/closed accordingly with 3 phases.In TPN breakers Neutral is closed forever,no control in it.It is my guess,If anybody find it mistake,Please give your correct answer.

Thanks&Regards.

ramanvadivelu

Reply
Anonymous Poster
#4

Re: 3 pole or 4 pole or TPN ACB (Air circuit breaker)

09/15/2008 6:57 AM

yes u can use,

just install a contactor of heavy rating , make it single pole , provide control coil supply from closing coil supply of ACB, any enjoy by converting 3P ACB tp 4P ACB.

BUT NEVER TRY TO SAVE MONEY IN MAIN DISTRIBUTION PANELS.......

Reply
Anonymous Poster
#6

Re: 3 pole or 4 pole or TPN ACB (Air circuit breaker)

09/17/2008 11:24 AM

es u can use an 3 pole acb instead of 4 pole acb,

but still u hve to give protection to neutral with the fast acting fuse circutry as rating depends on the laod u have

u can use the same neutral for both the supplys u have at the same time but dont any sacrifice with the main distribution panel

this is a guess

if u have more inductive (vqariable)load then it become harder to control it with tp acb and fast acting fuse for neutral

Reply
Associate

Join Date: May 2011
Posts: 38
#8

Re: 3 pole or 4 pole or TPN ACB (Air circuit breaker)

07/22/2015 1:54 PM

Dear Mr.Prashant,

I have the same problem consultant is asking for 4P for Generator Breaker , I dont want to provide him the 4 Pole Breaker because it is very costly .Please help us what reply i can give to the consultant , 4P is only use in case to disconnect from the neutral . so please advise what was your reply to that issue.

Regards

Amal

Reply
Reply to Forum Thread 8 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); koshy.dennis (1); North of 60 (1); prashanthng (1); RAMANVADIVELU (1); samsam_sam45 (1)

Previous in Forum: DC control supply V/s AC control supply for power control center (PCC)   Next in Forum: About VVVFD
You might be interested in: Circuit Breakers, Load Centers, Circuit Tracers

Advertisement