Anonymous Poster

Vacuum Interrupting Breakers

10/02/2006 6:13 PM

For Vacuum interupting breakers, how long the vacuum remain in acceptable level and how can be this tested for annual plant maintenance, and if the vacuum leaks how can be detected ASAP.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Member

Join Date: Oct 2006
Location: Kampala
Posts: 7
#1

Re: Vacuum Interrupting Breakers

10/03/2006 12:47 PM

Hi,

The vacuum is designed never to leak. However, a simple way to check if the sf6 is still in the VI is to pull the moving contact (open the VI). This motion should not be free but some resistance should be felt. On releasing the contact, it should 'spring' back into closed position and a distinct 'click' should be heard when the contacts make.

You could use a gas leak detector to check for leaks. A 5 year period is sufficient for CBs in normal operating conditions.

Let me know if you need more info'.

Regards,

Mbalu

Reply
Anonymous Poster
#4
In reply to #1

Re: Vacuum Interrupting Breakers

10/03/2006 11:41 PM

Hi there,

VI=Vacuum Interruptor. It's typically used in 11kV VCBs.

I don't see what is SF6 doing in a VI?

Have you mixed up those 2 types of circuit breakers?

Regards

OZ

Reply
Member

Join Date: Oct 2006
Location: Kampala
Posts: 7
#5
In reply to #4

Re: Vacuum Interrupting Breakers

10/04/2006 2:05 AM

OOpps! Sorry! Must have got mixed up. I meant the vacuum - not SF6. Have been working on 33kV 8DA10 breakers which use VIs in SF6. Sorry guys.

Nice day.

Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#2

Re: Vacuum Interrupting Breakers

10/03/2006 11:04 PM

In the glass ones, you can inspect the copper surface. Any gas entering causes the copper to get very thin layers of tarnish that have varied colors.

The sealed ceramic ones cannot be seen through, so the only way to tell if they have leaked is with a flashover tester. A vaccuum does not allow current fflow, so you apply the rated voltage (with a very high series resistance) and see what current draw there is.

Breakers like this are tolerant of flashover at very low currents, and cam even take brief high current flashovers from lightning etc.

__________________
Per Ardua Ad Astra
Reply
Anonymous Poster
#3

Re: Vacuum Interrupting Breakers

10/03/2006 11:08 PM

In the mining industry we use vauum interrupters extensively and will get literaly multiple thousands of cycles and up to 5/8 year of service. hope this helps! This type of interrupter is invaluable in higher voltages. Some very common voltages are : 480 olts, 575 volts, 995 volts, 2300 volts, 4160 volts, 7200 volts, 12470 volts, and 13200 volts.

Reply
Anonymous Poster
#6

Re: Vacuum Interrupting Breakers

10/04/2006 2:08 PM

The vacuum can be tested by applying a voltage test as recommended by manufacturer. With the contacts open, apply voltage across the contacts of the breaker. With a DC hipot tester the voltage can go up to 50 kV. If there is leakage in the vacuum , discharge will take place and the tester will trip showing a bad vacuum.

It is important to do this test during regular intervals such as annual maintenance. A leaking vacuum poses a serious operational hazard, as it will not be able to break the current during disconnection and may result in explosion of the vacuum bottle. However, upstream breaker will ultimately trip to remove the fault.

Reply