Ni-Cad Battery Sizing

09/22/2008 12:03 AM

The Load cycle of both NI-Cad Battery and Plante Battery is same.In that case what will be NI-Cad AH capacity (in percentage ) in relation to AH capacity of Plante Battery arrived on Load cycle. It is said that ageing factor of Plante Battery is 1.0 .What will be the ageing factor of Ni-Cad battery.Other details like over load, design margin remains same for both batteries.Is there any software available for sizing of Ni-Cad battery.

__________________
Best Regards
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2008
Location: TR
Posts: 142
Good Answers: 1
#1

Re: Ni-Cad Battery Sizing

09/23/2008 6:44 PM

Sorry but i've not heard about "Plante battery" as a kind of battery.

Might this be a habital phrase?

Register to Reply
Associate
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2007
Location: India
Posts: 42
Good Answers: 3
#2
In reply to #1

Re: Ni-Cad Battery Sizing

09/30/2008 6:51 AM

Plante Battery is one type of Lead Acid Battery with higher energy out put with Plante positive plates-99.99%lead with no ageing factor.These type of batteries are manufactured by EXIDE throughout .

__________________
Best Regards
Register to Reply
Active Contributor

Join Date: Feb 2011
Location: India
Posts: 19
#3
In reply to #2

Re: Ni-Cad Battery Sizing

04/06/2012 2:14 AM

Hello V.Ambarani,

For plante type batteries ageing factor is exactly - 1 because these type of batteries will provide their exact voltage(2.0V) upto its life time without any droop in voltage, but Nickel cadmium is not like Lead acid plante type, NiCd type of batteries the ageing factor is 1.25 because continuously usage of NiCd type of batteries will provide the less voltage so we need to give the 25% of ageing factor.

Thankyou,

One of the engineer trying to become best

__________________
Helping Hands Are Greater Than The Praying Lips
Register to Reply
Participant

Join Date: Jun 2012
Posts: 2
#4
In reply to #3

Re: Ni-Cad Battery Sizing

06/21/2012 1:57 AM

Please Note:

The grid of the positive plates will be corroded by the high charging potential:

Pb + 2H2O => PbO2 + 4H+ + 4e-

Left we see a cross section of a corroded spine of a tubular & PLANTE plate, with the PbO2-ring, which was corroded out of the lead.

Out of each Pb-Atom one PbO2-molecule is made. The addition of the two oxygen molecules increases the volume by 40%!

The larger size of the PbO
2-molecule forces the lead atoms to stay apart, i.e. the grid growths.

If the distance becomes to large, a lead atom jumps into the gap. In total a plastic deformation happens.

Maximum growth is 1-2%. A larger growth deteriorates the grid and can damage the lid.

So a spacell test is done in BS EN 6290-2-1999 Part 2 Specfication for the high-performannc Plante Positive type, so that the grouth is not more then 1 to 2 %, this test is not done in IS 1652.

PLANTE

Positive plate sets are hanging in the cell container supported by the cell balconies.

The negative plate set is supported from the bottom. The plate set is stands on the prisms.

Plate growth of the plate pack takes place toward to the cell bottom.

Positive plates of a Planté battery are hanging in the cell jar (balcony)

Negative plates are standing on a prism at the bottom of the jar.

This special design allows to observe the plate growth of the positive plate during lifetime.

If the positive plates reach the length of the negative plates, the Planté battery came therefore very close to their end of lifetime.

But if Plate grouth is only 1 to 2 % & the positive plate shading is also there, the life of positive plate is in process of lower capacity to it.

As per IEEE 485 Close: 6.2.3 Aging factor:

Please Note:

IEEE Std 450-1995 recommends that a battery be replaced when its actual performance drops to 80% of its

rated performance because there is little life to be gained by allowing operation beyond this point. Therefore,

to ensure that the battery is capable of meeting its design loads throughout its service life, the battery's rated

capacity should be at least 125% (1.25 aging factor) of the load expected at the end of its service life.

Exceptions to this rule exist. For example, some manufacturers recommend that vented batteries with Planté,

modified

their rated capacity (1.00 aging factor). These designs maintain a fairly constant capacity throughout their

life.

Planté, and round plate designs be replaced when their measured capacity drops below 100% of

This is not recumended by IEEE, but IEEE clearly sayes that it is "some manufacturers recommend".

But IEEE 1184 1994,

Annex A

Effects of elevated electrolyte temperatures o n commercial, vented lead-acid batteries applied to uninterruptible power system service.

Figure A.I shows the effects of temperature on battery life.

& acording to it it must be considerd.

So the Aging of PLANTE Battery must be as Tubular Battery as per IEEE 485, that's 1.25.

For NiCD Battery, please ask manufacturers to provide graph of Life V Capacity & select the Aging facter for the year you required the battery life.