How to calculate flue gas quantity (volume) from boiler inlet,boiler outlet and steam generated in a WHRB
Good Answers: 18
Re: Steam Calculations
09/24/2008 11:27 PM
I would suggest it is more appropriate to obtain the flow (weight/hr), fuel composition and Orsat analysis of the combustion gases as well as discharge temperature in order to make this determination.
United States - Member - Member Engineering Fields - Power Engineering - New Member
09/25/2008 9:06 AM
Orsat is a very good excercise, but if only inlet and outlet flows are needed a simpler approach could be the "Million-BTU Method."
F = 10^4(100-%ash - %solid fuel loss)/HHV
Awet = ((11.68(%c) + 35.03(%H - %O/8) + 4.38(%S))/HHV)10^4
C = 1 - (%solid combustible weight loss)/100
P = F + CA
P= Total gaseous products, lb / 10^6 Btu
F = fuel fired less ash and loss, lb / 10^6 Btu
A = Atmospheric air, lb / 10^6 Btu
C = Combustible loss factor
Reference "Combustion Fossil Power," 4 ed, Singer
09/25/2008 9:02 AM
What is the source producing the waste heat? Is there supplementary firing before the WHRB? A little more info would be helpful.