Digital timer outlet loses program

10/04/2008 1:50 AM

I purhased two inexpensive digital timer outlets to turn on a small centrifugal pump for one minute several times each day. When the pump turns on, the timer loses its program and time as if a surge fried its memory. The second timer worked fine controlling a lamp and small fan but the same thing happened with I used it to control the water pump. Any ideas why turning on the pump would cause the timer to lose its memory?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Associate

Join Date: Aug 2006
Location: Phoenix Arizona
Posts: 44
Good Answers: 13
#1

Re: Digital timer outlet loses program

10/04/2008 2:50 AM

Several problems come to mind.

The pump motor has ratings higher than the timer can handle. Check the ratings listed on each. Current draw can be higher than listed ratings at motor start up when the motor is started under load.

The timer is not rated for inductive loads. Electronic timer circuits don't like this. The lamp is a resistive load while the pump is inductive.

Some motors produce a back current when power is cut. This is caused by the collapse of the magnetic field of the motor. Electronic circuits don't like this either.

Look into timers designed to be used for pumps. Intermatic is just one such company.

Good luck

__________________
"If you need a machine and don't buy it, then you will ultimately find you have paid for it but don't have it" - Henry Ford. (Also my excuse when adding to my ever expanding collection of tools)
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#2

Re: Digital timer outlet loses program

10/04/2008 3:15 AM

AS Avi-tech said, specifically EMC issues, spikes resulting from switching inductive loads can easilly cause microcontrollers to reset or set them into unwanted modes where they write to memeory.

Try some suppression on the leads to the load, a nice chunky ferrite like you see in power supplies for laptops, a capacitor (suitably rated) across live and neutral will help too. If you are not into electronics then you can buy a filter. Make sure the incomming supply to the timers is filtered too.

You could always run a test by using the timers on a more passive load (say a table lamp) and see if the still fail...that would indicate that the problem is the incomming power...not the load.

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#3

Re: Digital timer outlet loses program

10/04/2008 11:54 AM

As AT & Del said the timer may not be able to handle load. You could purchase a motor starter that could handle the pump motor load and have the timer switch it.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Anonymous Poster
#4

Re: Digital timer outlet loses program

10/04/2008 1:55 PM

Thanks for the helpful explanations. The inductive load explanation is really helpful. The aquarium pump is very small so I don't think it's a load issue. I'll look for a better built timer designed for both resistive and inductive loads. Thanks again.

Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#5

Re: Digital timer outlet loses program

10/05/2008 11:43 AM

Don't know if you can do this or not but one thing that can help you is just remove operating replay from inside and fix it somewhere outside.

Also put a spike suppressor at the VCC of timer.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#6

Re: Digital timer outlet loses program

10/05/2008 5:06 PM

Timer,

I had a problem with a PLC output controlling a buzzer. It would time and then unpredictably reset when the buzzer was on. Turned out that the buzzer was putting electronic noise back into the PLC through the output. When I changed it so the output was controlling a relay coil and the buzzer was wired through the relay, the problem disappeared.

Therefore, you can look at the type of load the pump represents. It is possible that it is introducing noise back to the timer. Another possibility is that the inrush current for the pump is momentarily causing a voltage sag, which is causing the timer to lose its memory.

I think that the external relay is the best approach to solving the problem. Inexpensive digital timers can easily have a design which leaves them susceptible to noise, voltage sags, or similar woes.

--JMM

Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); avi-tech (1); jmueller (1); ozzb (1); rakesh_semwal (1); user-deleted-1105 (1)

Previous in Forum: Senior Project Help   Next in Forum: HOW DO I DESIGN A 5000KVA{230V,50HZ}NVERTER.
You might be interested in: Flash Memory Cards, SRAM Memory Chips

Advertisement