SPAJ 140C Relay Tripping

10/09/2008 2:00 PM

A 250KVA transformer was replaced with a 500KVA. Each time the transformer was powered, the SPAJ 140 relay on the HV ( Primary side ) always trips off immediatly or at most after 20 seconds. The transformer has been checked for winding earthfaults but was comfirmed O.K. What is the possible cause of this triping.

A secondry injection test was done on relay and its O.K

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Aug 2006
Posts: 183
Good Answers: 2
#1

Re: SPAJ 140C Relay Tripping

10/10/2008 2:41 AM

Dear Friend

Primary current & surge current of 500 kVA transformer is twice that of 250 kVA transformer, assuming even the transformer % impedance is same for both.

Thus pls. check current settings of the relay. I donot know anything about SPAJ 140 relay & hence cannot comment on its suitablity for 500 kVA transformer.

Thanks and regards

Ashok Toshniwal, Bangalore, India

Register to Reply
Member

Join Date: Oct 2009
Posts: 8
#6
In reply to #1

Re: SPAJ 140C Relay Tripping

10/24/2009 4:05 AM

guys i need ur help .. if my ct is 300/5 and the minimun setting of aab spaj140c for low set is"I>" is (0.5 X In) where (In is the secondary of the current transfomerand fixed In=5 ) plz can y tell me wats the minimum Phase current if i select 0.5

according to me its 150 amp .... is it rite or wrong ..?? i need ur help as early as possible

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jul 2008
Location: Finland
Posts: 22
#2

Re: SPAJ 140C Relay Tripping

10/10/2008 2:57 AM

Two possibilities:

- magnetizing inrush current is doubled -> instant tripping after transformer is powered.

- your load amperage has risen -> overcurrent relay tripping is set too low

Solution: Check your overcurrent relay settings to correspond new transformer.

Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#3

Re: SPAJ 140C Relay Tripping

10/10/2008 11:00 AM

As stated in one of the replies; all of the primary current dynamics would double when replacing a 250KVA unit with a 500KVA unit. If your relay settings have been changed accordingly and verified by testing to be correct (including the time curve) then you need to look at the many other probable causes.

Have you tried energizing the transformer without the secondary connected to eliminate the possibility of excessive secondary loading?

Are you sure that the time curve is adequate for meeting the inrush demand?

Have you performed a Turn-to-Turn Ratio (TTR) Test on the transformer to verify the windings?

Have you performed a Doble and/or HyPot test on both the primary and secondary winding to check for faults other than grounds?

Reputable electrical testing vendors also have the capability of performing a surge test on your equipment that will identify any shorting between winding conductors and phase-to-phase faults. The cost is very reasonable when compared to unit replacement and it will establish a good "basepoint" for future testing reference.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#4

Re: SPAJ 140C Relay Tripping

10/10/2008 2:11 PM

I suspect that the relay just needs adjusting to accommodate your new transformer. Your transformer may have a higher leakage than your previous unit. See http://www.abb.com/product/db0003db004281/c12573e700330419c225695f003ae92b.aspx for a list of literature for this relay. You might find the answer to your problem here.

Register to Reply
Member

Join Date: Oct 2009
Posts: 8
#5

Re: SPAJ 140C Relay Tripping

10/24/2009 4:04 AM

guys i need ur help .. if my ct is 300/5 and the minimun setting of aab spaj140c for low set is"I>" is (0.5 X In) where (In is the secondary of the current transfomerand fixed In=5 ) plz can y tell me wats the minimum Phase current if i select 0.5

according to me its 150 amp .... is it rite or wrong ..?? i need ur help as eaqrly as possible

Register to Reply Off Topic (Score 5)
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ashoktoshniwal (1); Flux (1); Lendog (1); sarmad786 (2); SHOCKISCAN (1)

Previous in Forum: impedance   Next in Forum: Electromagnet Strength

Advertisement