Anonymous Poster

Capacitors and Three-Phase Conversion

10/09/2008 4:26 PM

A few years ago I built a phase converter for My shop. It worked fine until I sold the shop, now they are having problems with it.

I used a 3 h.p. 3 phase motor to generate the 3 phase power. I traced everything down to possibly the capacitor in the circuit. The capacitor that I have is a 710-850 mfd 125vac. when I try starting the motor it just hums and the shaft barely turns. My question is How do I determine if the capacitor is good. Also in the schematic the the capacitor is listed as 220 voltac. does this make a difference. seems to Me this was the original capacitor that I used.

oilcan13

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Capacitors and Three-Phase Conversion

10/09/2008 9:19 PM

"when I try starting the motor it just hums and the shaft barely turns."

Assuming you mean when you start the single phase motor. What you are describing is usually a symptom of the centrifugal start switch in the 1 phase motor being open. It is what applies the start capacitor to get the motor spinning when you start it up. As the motor comes to speed, the centrifugal force opens the switch and drops out the start cap. If the switch fails to reclose when you shut it off, the start cap is not there and the motor just hums.

You may be able to repair it if you are good with mechanical parts, but I have tried and failed, it's trickier than it appears. I would take it to a motor shop, they do that all the time and will not likely charge you much.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Associate

Join Date: Jan 2008
Posts: 34
#3
In reply to #1

Re: Capacitors and Three-Phase Conversion

10/10/2008 1:15 AM

He's not running a single-phase motor. He's running a three-phase motor to generate a third leg. Most phase converters use caps for this along with a timer/starter switch to charge the caps enough to provide a current to the L3 of the converter motor just long enough to get that motor turning and generating an L3 through induction. That humming noise he's describing is classic single-phasing, so he's looking at either a bad capacitor, a bad motor, or possibly insufficient current on L1 or L2.

That VAC rating will, IIRC, make a difference. When using a 125VAC cap in a 220VAC circuit, cut the farad rating in half. Some meters have the ability to test a capacitor; if you don't have one, an A/C repair shop might be able to help you out. But I'm pretty sure if it was bad you'd know it...the lid would be blown out and the interior's packing material would be leaked all over the place.

So -- check those caps. Heck, replace them if you're worried about it. I don't think they're that expensive. Meg that motor and check your line voltage. If all else fails, get you a VFD (they can generate an L3 for you) and ditch that phase converter. That's what I finally did with mine, and believe me, it was the best money I ever spent.

Reply
Anonymous Poster
#8
In reply to #3

Re: Capacitors and Three-Phase Conversion

10/11/2008 8:07 AM

Thanks for the great advice. You seem to know what your talking about and understand My question.

One other question . What is a VFD?

Thanks

oilcan13

Reply
Associate

Join Date: Jan 2008
Posts: 34
#9
In reply to #8

Re: Capacitors and Three-Phase Conversion

10/11/2008 9:55 AM

Happy to help, believe me. I had a phase converter -- two different ones, actually -- on a lift station of mine for years. Had to baby that thing like you wouldn't believe some times. It felt like all I had to do was look at it at times and it would blow caps. When I was finally able to get rid of it, I did and never looked back.

A VFD is a variable-frequency drive. These, through varying current frequency and voltage, allow motors to be run at variable speeds. They can also generate a third leg, just like a phase converter but without having to worry about caps. Note that if you go that way, you'll need to look at a drive with a horsepower rating twice that of the motor; i.e. a 3HP motor will need a 6HP drive. Still, worth it in my opinion.

Reply
Power-User

Join Date: Jul 2007
Location: Somewhere in the hills of Pennsylvania, I think.
Posts: 246
Good Answers: 4
#2

Re: Capacitors and Three-Phase Conversion

10/10/2008 1:04 AM

Sounds like the capacitor is open. Time to replace it. The capacitance value sounds high for 3 HP but the voltage is too low. You need at least a 250V cap. the higher voltage rating, the better. You should have a potential relay in that circuit also, you need to check that it is functioning properly also.

__________________
I'm somewhere between the age of thirty-something and Alzheimer's. I just can't remember where!
Reply
Anonymous Poster
#5
In reply to #2

Re: Capacitors and Three-Phase Conversion

10/10/2008 7:55 AM

This is a little off subject but, when running a three phase motor on single phase, is there any derating of the horsepower of the three phase motor? I know that to use a VFD for this it needs to be increased.

Reply
Power-User

Join Date: May 2008
Location: Europe
Posts: 285
Good Answers: 9
#6
In reply to #5

Re: Capacitors and Three-Phase Conversion

10/10/2008 8:16 AM

Dear Guest, I would expect that running a three phase motor from a single phase supply (once you have managed to start the three phase motor) it would only generate about 2/3 of its rated power since you are only using two out of the three windings.

However if you are using a VFD then the VFD will generate the three phase from the single phase so I would not expect a decrease in power from the three phase motor.

Not sure if this answers your query or not.

These are just my thoughts and I am liable to be incorrect. Perhaps someone can either confirm or correct my thoughts.

Kind regards

Mr. W.A Snow

Reply
Anonymous Poster
#10
In reply to #6

Re: Capacitors and Three-Phase Conversion

10/11/2008 5:26 PM

Thanks for the input. All the info I had on converters was That a static converter would generate 2/3 the power needed but that a rotory converter would generate the full amount. i.e. a 3hp 3 phase motor will start and run a 3 hp 3 phase motor where as a static converter rated at 3 hp would only start and run a 2 hp 3 phase motor.

is this correct thinking?

oilcan13

Reply
Power-User

Join Date: Jul 2007
Location: Somewhere in the hills of Pennsylvania, I think.
Posts: 246
Good Answers: 4
#7
In reply to #5

Re: Capacitors and Three-Phase Conversion

10/10/2008 9:13 AM

You will get only 2/3 of the rated hp. In this case, he is using the motor to generate or manufacture the missing third leg in order to supply 3 phase to other equipment.

__________________
I'm somewhere between the age of thirty-something and Alzheimer's. I just can't remember where!
Reply
Power-User

Join Date: Oct 2007
Posts: 397
Good Answers: 3
#13
In reply to #2

Re: Capacitors and Three-Phase Conversion

10/14/2008 8:38 AM

I replaced the capacitor and it now works.

However I replaced it with one similar that I had which was 750-800 mfd @120 volts.

My thinking might be wrong on this but the capacitor is in a 120volt circuit suppling voltage to the third leg of the three phase motor that is why I was hesitant about putting in a 220 volt capacitor. Would a 220 v capacitor work in this situation?

Any comments are welcome.

oilcan13

Reply
Power-User

Join Date: Jul 2007
Location: Somewhere in the hills of Pennsylvania, I think.
Posts: 246
Good Answers: 4
#14
In reply to #13

Re: Capacitors and Three-Phase Conversion

10/14/2008 8:51 AM

The 120 volt cap should work for a while. When it goes, replace it with one rated for 250v. In this case, the voltage rating has nothing to do with the amount of energy passed, only the strength of the internal insulation (electrolyte). That capacitor is working in a 230 volt circuit and should have a rating of 250 volts (or more). Hope this helps.

__________________
I'm somewhere between the age of thirty-something and Alzheimer's. I just can't remember where!
Reply
Power-User

Join Date: May 2008
Location: Europe
Posts: 285
Good Answers: 9
#4

Re: Capacitors and Three-Phase Conversion

10/10/2008 1:36 AM

Dear Guest, is this what you have built http://www.metalwebnews.com/howto/phase-converter/phase-converter.html or something like it. Perhaps this article might assist you with your current issue.

Regards

M.r. W.A. Snow

Reply
Power-User

Join Date: Oct 2007
Posts: 397
Good Answers: 3
#11
In reply to #4

Re: Capacitors and Three-Phase Conversion

10/12/2008 8:05 AM

Thanks:

I went to the web site and found the explanation very explicit, however the sketches left somthing to be desired, I could not read the notations on the sketches.

Thanks anyway

oilcan 13

Reply
Power-User

Join Date: May 2008
Location: Europe
Posts: 285
Good Answers: 9
#12
In reply to #11

Re: Capacitors and Three-Phase Conversion

10/12/2008 12:16 PM

oilcan13, yes the scetches were very poor but I though that the explanation was quite OK.

Regards

Mr. W.A Snow

Reply