AHU Chilled water coil temperature details ...

10/16/2008 9:51 AM

AHU Chilled water coil temperature details ...?.

chilled water coil in AHU ,

1) what will be the Wet bulb & Dry Bulb temperature of air passing thru coil in the AHU.

2) what will be the chilled water in & outlet temperature in the AHU cooling coil?.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: AHU Chilled water coil temperature details ...

10/16/2008 10:57 AM

This depends on your geographical location . For office or laboratory . Your question is too broad .

Register to Reply
Anonymous Poster
#2
In reply to #1

Re: AHU Chilled water coil temperature details ...

10/16/2008 11:31 PM

there will be depend on the humidity you are looking for and the air volume passed the cooling coil,

Register to Reply
Active Contributor

Join Date: Sep 2008
Posts: 10
#4
In reply to #2

Re: AHU Chilled water coil temperature details ...

10/16/2008 11:42 PM

location of AHU IS IN LAGOS-NIGERIA & AHU is for PHARMA HVAC CLEAN ROOM of 100k.

I require inside AHU conditon of WET & DRY bulb temp.

from chiller if it is chilled water flowing in cooling coil 7Deg.C coming out of AHUI cooling coil is 12Deg.C, then what will be the inside AHU before & after cooling coil wet & dry bulb temp.

humidity in the room is RH-less then or equal to 55%. and air volume acroos different AHU 4500cfm to 12000cfm flowing across coil.

Register to Reply
Active Contributor

Join Date: Sep 2008
Posts: 10
#3
In reply to #1

Re: AHU Chilled water coil temperature details ...

10/16/2008 11:40 PM

location of AHU IS IN LAGOS-NIGERIA & AHU is for PHARMA HVAC CLEAN ROOM of 100k.

I require inside AHU conditon of WET & DRY bulb temp.

from chiller if it is chilled water flowing in cooling coil 7Deg.C coming out of AHUI cooling coil is 12Deg.C, then what will be the inside AHU before & after cooling coil wet & dry bulb temp.

Register to Reply
Associate

Join Date: Dec 2006
Location: Silverdale, Washington
Posts: 29
#6
In reply to #3

Re: AHU Chilled water coil temperature details ...

10/17/2008 3:02 AM

Do you have any idea what your question is?

It makes no difference where in the world you are!

It makes no difference what in the world you are trying to cool!

LAT can not be calculated without proper data!

If you have an AHU than give us the specifications for it.

If you have a water cooling coil give us its specifications.

Do you know the ΔT ( Delta-T) of the chilled water is 5º C? Or is that some kind of fabrication?

Do you know the flow rate of the chilled water?

With the data you have provided I could provide any answer the shows some cooling and I would be right.

EAT is a start. DB & WB

AHU air volume is needed.

__________________
There may be no stupid questions - Some are just poorly contrived !
Register to Reply
Associate

Join Date: May 2007
Location: Australia
Posts: 27
#5

Re: AHU Chilled water coil temperature details ...

10/16/2008 11:52 PM

The first part of your question has been answered. the second part of your question; the chilled water flow/return from chiller is usually 44/55oF.

For first part you need to use psychometric chart, knowing the elevation of place you are doing the calculation for and other required parameters of the city plus the space which you doing calc for (RH, Temp. ,...).

__________________
Never laugh at anyone's dream. People who don't have dreams don't have much.
Register to Reply Off Topic (Score 5)
Associate

Join Date: Jan 2007
Location: Los Angeles, California
Posts: 35
Good Answers: 3
#7

Re: AHU Chilled water coil temperature details ...

10/17/2008 6:26 AM

Rajuas, the others are correct, you have not submitted enough data for anyone to provide an answer, however here is a partial answer.

Cooling capacity matches the building heat load, not the airflow. However, since you know the temperature rise of the water (7C to 12C) you can calculate the heat load if you know the quantity (water flow) of the water.

Coils are custom made to remove a certain amount of sensible heat (temperature) and latent heat (moisture). Thus a coil for a dry desert would be constructed differently than a coil for a humid tropic area.

You stated the relative humidity of the space, but not the temperature. Also, you did not mention if there was any outside air that would increase both the temperature and humidity of the air across the coil.

However, for a very rough answer, assume that the air entering the coil is about 23C and 55% RH. The air leaving the coil might be about 13C and 99% RH. Good luck with your calculations.