Flange Protection

10/20/2008 6:52 AM

We have 16-inch weld-neck flange class 150 (Carbon Steel) installed at overhead Gasoline pipeline, this pipeline is running over hazardous location where flammable materials are there and fire could occur any time. We need to protect this flange against leakage with fire proof material. Do you recommend any product for this application or any idea that could help?

Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Flange Protection

10/20/2008 11:10 PM

It would be better to relocate the flange away from the area. Else, try this:

http://www.ramco-safetyshields.com/html/metal.htm

Register to Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Aug 2008
Location: Europe
Posts: 287
Good Answers: 27
#2

Re: Flange Protection

10/20/2008 11:22 PM

Hello Elak, I understand your concern. However, before you start thinking about how to contain a leak, I respectfully suggest that you might want to do everything possible to prevent such a leak.


A suitable gasket, compressed under sufficient load, between proper seating surfaces, and clamped by bolts of an appropriate size and material is only the beginning. A critical component, often overlooked is how the load is going to be applied. Often this is done by "torquing" the bolts. Unfortunately, if this is done without proper load verification (by measuring the resultant bolt stretch, for example) the integrity (and safety) of the joint is at risk: Bolt "torque" is only a measurement of resistance to input force. Contrary to what many believe, it is not an indication of a bolt's "tightness". In fact, one bolt accurately "torqued" to a prescribed specification could be dangerously loose while another one "torqued" to the same specified "torque" may be tightened to beyond its yield point!


Lots to think about...!

__________________
Best regards, HeviiGuy
Register to Reply
Participant

Join Date: Aug 2008
Posts: 2
#3

Re: Flange Protection

10/21/2008 2:21 AM

And maybe you can use our heat shrink pipeline sleeving to protect your carbon steel.and detail you can check:http://en.changyuan.com/Catalog_39.aspx

Henry

Register to Reply
Anonymous Poster
#4

Re: Flange Protection

10/21/2008 4:30 AM

What about aerogel seal

Register to Reply
Anonymous Poster
#5

Re: Flange Protection

10/21/2008 5:02 AM

I hope for such cases, ring tight joint (RTJ) to asme should be ok since the seal is a pure metal ring.

dimensions for the flanges as well the seals are available in the standard.

regards

thyagarajan

Register to Reply
Associate

Join Date: Feb 2008
Posts: 52
Good Answers: 1
#6

Re: Flange Protection

10/21/2008 7:08 AM

Elak,

you do not want to encapsulate the joint, you want to CONTROL it, it must be visible. The liquid does not burn, the vapour does when the concentration is enough. Do not make a bomb, if you suspect that flange is not reliable, then redesign it...

Good luck.

Register to Reply
Commentator

Join Date: Nov 2007
Posts: 62
Good Answers: 1
#7

Re: Flange Protection

10/21/2008 7:30 AM

Sounds to me like this is a location for a proper welded joint with flanges, if needed for maintenance reasons, located safely away from the ignition source.

Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#8

Re: Flange Protection

10/21/2008 9:35 AM

As others have suggested, if the flange is really a problem, you should get rid of it and probably re-route the pipe. The real trick though would be to keep a fire from starting in the first place. What mitigation efforts are you putting in place to keep the hazards in the location minimized?

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Anonymous Poster
#9

Re: Flange Protection

10/21/2008 10:27 AM

Re-route, re-route, eliminate the doubt!!!

Register to Reply
Participant

Join Date: Oct 2008
Posts: 3
#10

Re: Flange Protection

10/21/2008 12:24 PM

As already opined by comembers, the best option is to reroute, or if the route cannot be changed, to have a continuous pipe without joint over the fireprone area.

However, if this cannot be avoided,
we can supply special gaskets which tighten under fire,
and we will re-engineer the joint.

But in the event of a fire, after the fire is doused, the joint will need complete replacement if it has to survive another fire.

Kindlly contact offline at havewala@gmail.com, skype NMHavewala.

NMHavewala

Mazda Manufacturers

Bombay, India.

Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#11

Re: Flange Protection

10/21/2008 6:46 PM

iI also believe the best route is to relocate. If not possible, there have been many good suggestions mentioned. I would suggest when you have applied whatever improvements you have decided to make, consider this. A secondary containment system. A trough that will catch any drips that might develop, and rout to a central location to monitor. Or a sensor in the trough to sound an alarm. In the event of a small leek, it might avoid a much larger problem.

__________________
Bob
Register to Reply
Guru
Popular Science - Evolution - New Member

Join Date: Jul 2006
Location: India-Chennai.
Posts: 722
Good Answers: 30
#12
In reply to #11

Re: Flange Protection

10/22/2008 12:58 PM

Inside the heaters, furnaces and reformers tubes/pipes with inflammable hydrocarbon fluids crisscross for heat transfer purpose. These tube are well designed for such purpose.

So well designed pipe/tube should be all right for this service with due consideration of not having flanged, threaded joints. Going for higher class will also help.

__________________
A picture worth thousand words: needless to say if it is animated.
Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#13
In reply to #12

Re: Flange Protection

10/22/2008 3:00 PM

How well designed is it if it has a flanged joint above a dangerous area?

__________________
Bob
Register to Reply
Guru
Popular Science - Evolution - New Member

Join Date: Jul 2006
Location: India-Chennai.
Posts: 722
Good Answers: 30
#14
In reply to #13

Re: Flange Protection

10/23/2008 4:08 AM

Yes, I agree your point, Flange joint should not be included in the envelop of dangerous area.

I said, "well designed pipe/tube should be all right for this service with due consideration of not having flanged, threaded joints."

__________________
A picture worth thousand words: needless to say if it is animated.