Y Start, Delta Run, No Starting Torque

10/23/2008 12:03 PM

Long time lurker, first time poster, my location is United States.

One of our customers has had a puzzling problem with a piece of equipment.

The equipment was purchased, used, last year and since it was installed, has been operating well until recently. I am uncertain of the age of the equipment, but the control panel uses an Allen Bradley SLC 150, Logic Control equipment that has been obsolete for many years already, so this gives an indication of it's age.

The equipment is a decanter with a 30KW (40 HP) motor. It's nameplate is 230/460V, 49A, 3535 RPM, 60 Hz, 3 Ph. It has 12 motor leads.

All wire sizes are correct according to the NEC, and the control panel was wired according to the manufacturers drawings.

The motor is connected to the load using 8" OD drive pulley and 9" OD driven pulley, using a matched 3 belt set. The load is a high inertia decanter.

The electrical starting sequence is a typical "Y" start, Delta run configuration, with a timer to control the "Y" start time.

We were called in when the motor would not start up properly.

When the system is started, the main motor contactor closes, and the "Y" start contactor closes. The motor draws approximately 70 Amps on all three phases, phase to phase voltage is approximately 460VAC on all three phases, but the motor will not rotate at all with the drive belts attached. If the drive belts are removed, the motor will "slowly" come up to speed, but in either case, the motor does not appear to have any appreciable start-up torque. After the designated "Y" start time, the configuration switches to Delta run, and the motor will start to rotate, but will trip off on over-current after a few seconds.

After inspection, all appears to be in good order with the panel feeders, and panel wiring. The motor contactors were disassembled and inspected and appear to be in good order, with suprisingly little wear on the contacts. Contactor coils all measure good resistances.

We tested the motor on-site and all motor terminations appear good, a motor megger test was performed both from the panel and locally at the motor termination box, which showed good. Winding resistance tests also showed good both from the panel and locally. Running out of ideas, we began to suspect that perhaps the rotor shorting bars had open-circuited.

The motor was removed and brought to a local repair/rewind shop that we have used before with good results. The technicians disassembled the motor and other than a drive end bearing that they say made a little growling and was was replaced, have tested the motor as follows:


Visual inspections of stator and rotor are good,
Hi-pot tests are good,
Motor winding resistance tests are good,
Motor rotor magnetic tests show no problems with the rotor shorting bars of the squirrel-cage rotor,
Motor has been connected in their shop and run in a high-voltage Delta configuration, with no load, and they say the performance is acceptable.

The repair shop has improvised a low-voltage torque test. They used approximately 120VAC as a test voltage from an 3 phase auto-transformer, and achieved approximately 16 lb-ft, in a stalled rotor test. Assuming torque is linear, they say this would calculate out to approximately 64 lb-ft of torque. The motor torque calculated from horsepower is approximately 60 lb-ft. According to Stallcups's Generator, Transformer, Motor and Compressor book, the auto-transformer configuration they used will give the same effect as full-voltage starting, with good torque characteristic, which would explain their results.

After the repair shop's inspection, the motor was re-installed and re-tested with the same previous results, almost zero starting torque in "Y" start configuration.

We then reconnected the motor using a high-voltage Delta configuration to a Variable Frequency Drive. The motor is now functioning correctly and does not seem to suffer any lack of torque on start-up with the VFD driving it.

My question is, why would the motor all of a sudden display no appreciable torque with a "Y" start, while all windings test out normal both on-site and at the repair/rewind shop, but then operate normally when connected to a VFD in Delta configuration?

__________________
All rights reserved. Lefts served only once.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Y Start, Delta Run, No Starting Torque

10/23/2008 2:43 PM

Most likely, the motor connections for Y-Delta starting were incorrect. it's a very very common problem and one of the reasons I NEVER spec Y-Delta as a starting method. In IEC countries it is used all the time and everyone is used to it. But in the US, many electricians are never trained on how it works and have no clue what the diagrams mean in the motor connection box, so they end up miswiring it. A 12 lead motor makes it even more difficult because it is a dual voltage motor, so there is even more potential confusion there.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member Hobbies - CNC - New Member

Join Date: Aug 2006
Location: Western Australia
Posts: 767
Good Answers: 58
#2

Re: Y Start, Delta Run, No Starting Torque

10/23/2008 9:12 PM

How I wish everyone would ask questions as clearly as this. If there was a GQ rating I would give you one.

Unfortunately no help from me, except to say that when I was an apprentice I had to work on many of these things and if they did not work it was always because I had made a mistake when wiring the control panel.

__________________
If you can't explain it simply, you don't understand it well enough. (A.E.)
Register to Reply
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#3
In reply to #2

Re: Y Start, Delta Run, No Starting Torque

10/23/2008 10:34 PM

I agree, definitely deserves an award for the best described problem.

I am still perplexed why it ran fine for a long time THEN exhibited the low torque fault.

__________________
johny451
Register to Reply
Anonymous Poster
#4

Re: Y Start, Delta Run, No Starting Torque

10/24/2008 12:56 AM

Since it ran on delta, the motor and power circuit must be right. Check again the star connectiions it must be wrong.

shivaram

Register to Reply
Commentator
Australia - Member - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jan 2008
Location: Mount Gambier, South Australia
Posts: 56
#5

Re: Y Start, Delta Run, No Starting Torque

10/24/2008 1:59 AM

G'day Livewyre,

The 12 motor leads makes me curious, normally we only come across 6 in most motors.

Anyway, it is interesting, if no one has 'touched' the motor wiring, and it was starting in star fine before this, you have to think the wiring is correct. And it is normally when it switches into Delta where motor wiring faults will show up.

Are you able to disconnect the load, or reduce it, and see if it starts? Maybe there is a load issue, and in star the motor torque is a fair bit lower anway. Also I would have thought that you should see more that 70 amps with a stalled rotor in star.

With the VFD on the motor, what does the starting current look like? High for a while? What is the ramp settings, and did you need voltage boost? Possibly the VFD is starting the motor with higher torque than the star/delta starter.

Cheers,

Trevor.

__________________
tooz
Register to Reply
Anonymous Poster
#6

Re: Y Start, Delta Run, No Starting Torque

10/24/2008 4:11 AM

Reason for "No starting torque":

------------------------------

The torque developed in the motor is proportional to the square of the applied voltage. In your case, the load being a high inertial one, the voltage applied across the windings when they are connected initially in Star is definitely not sufficient enough to produce the required starting torque of load.

Hence I conclude that the voltage required to produce enough starting torque is above the Star voltage.

Reason for tripping in Delta:

--------------------------

The Delta voltage must be sufficient for delivering the required torque. But why did the motor tripped within some time after delta changeover? The answer is, as the motor had not accelerated enough in Star, the I2t would have already reached a higher valve and by the time it changes over to delta it would have reached the tripping limit.

Solution:

-------

A starting method which can give a voltage more than Star voltage at start will solve the problem. A soft starter ( Series reactor type or Thyristor type with higher voltage output at start) will be enough to solve the problem.

Since VFD also have function of soft starter, you problem has been solved.

Hope puzzles are solved.

R. Nagaraj,

India

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2007
Posts: 24
#7

Re: Y Start, Delta Run, No Starting Torque

10/24/2008 1:49 PM

Sounds like there may be a capaciter bank in the system mabe for the power correction that has gone bad.

Register to Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#8

Re: Y Start, Delta Run, No Starting Torque

10/24/2008 10:10 PM

The answer to this may not lie with the motor. How were the various contactors of the starter?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#9
In reply to #8

Re: Y Start, Delta Run, No Starting Torque

10/25/2008 10:14 AM

I read your original post over again and saw where you mentioned the inspection on the contactors.

What was the state of the power factor on the 3 phase supply to the reduced voltage starter? I seem to recall reading once upon a time that power factor issues can impact starting torque on Y start Delta run reduced voltage starters. What the issues were escape me, but I'll try and research it.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Associate

Join Date: Feb 2008
Posts: 49
Good Answers: 5
#10

Re: Y Start, Delta Run, No Starting Torque

10/25/2008 11:24 AM

MY GUESS is the following, and I do mean guess, because it's from overhearing comments made by my father, the electrician:

The motor was wired up with the three phases out of sync with each other.

Now I'll check the other answers to see if that has been given. If not, I'll return and explain myself better.

Register to Reply
Associate

Join Date: Feb 2008
Posts: 49
Good Answers: 5
#11

Re: Y Start, Delta Run, No Starting Torque

10/25/2008 11:29 AM

Okay, I forgot that the motor had been working fine for awhile.

I'm still stuck on the idea that the three phase wiring somehow got out of sync with one another.

Perhaps an electrician moved one of the leads in the distribution box, while doing some other work?

As I said before, this is really out of my league.

Register to Reply
Associate

Join Date: Jul 2006
Location: OZ
Posts: 33
Good Answers: 3
#12

Re: Y Start, Delta Run, No Starting Torque

10/26/2008 10:07 PM

Excellent description, but I have one more question.

Did the motor ever work in this application???

If so, following all your test results, it would indicate

An error in the delta wiring connections of the motor or the control panel

This motor has two sets of winding per phase because of dual voltage.

Depending on the working voltage the winding are connected in

series or parallel

If the motor was never used in this application and the wiring is OK,

it would be possible that motor starting torque is low.

But if it is OK with a VSD, should be OK with a star/delta system

__________________
Shocking from OZ
Register to Reply
Guru
Popular Science - Weaponology - New Member Hobbies - Fishing - New Member

Join Date: May 2007
Location: Aloha or
Posts: 659
Good Answers: 19
#13

Re: Y Start, Delta Run, No Starting Torque

10/27/2008 12:40 PM

One item i did not see mentioned is that your starting torque requirements may have gone up. The system may have changed so that there is more resistance to starting now than there was when is was first installed.

__________________
Closed biased minds are utterly impervious to any factual evidence which contradicts their beliefs
Register to Reply
Power-User

Join Date: Nov 2006
Location: antwerp/belgium/europe
Posts: 160
Good Answers: 5
#14

Re: Y Start, Delta Run, No Starting Torque

10/27/2008 12:50 PM

Yes indeed ... perfect explanation ... *s* ... but ... one diagram might say more than a thousand words ... *s*

And wasn't there more info on the motor's name plate ? Maybe we're talking here about a so called "Dahlander" motor. This motor has 2 windings for every phase. (to have two speeds) These windings can be put in series or parallel or used individually. The windings (in parallel or in series) can be in star or delta ... We talk about Y/Δ or YY/ΔΔ

The 12 leads and the 230/460 made me think of a Dahlander. Usually for standard motors we have 230/400, no? (factor SQR(3)). 460 = 230 x 2 ! (windings in series ?)

Anyhow : good luck !

__________________
44mEurope
Register to Reply
Participant

Join Date: Oct 2008
Posts: 3
#15

Re: Y Start, Delta Run, No Starting Torque

12/16/2008 4:59 PM

Thank you to all who replied or submitted answers and opinions. I just wanted to update the information and provide some closure.

The problem was first noticed about 3 weeks prior to my post. I took phase-to-phase voltage readings, but I admit I didn't pay much attention to them other than seeing that they were all around 4XX Volts. I was convinced that the problem was with the motor rotor, and did not leave myself open to other conclusions.

Upon closer examination, after reading most of the posts, we brought in a 3-phase power analyzer and found that A-B = 487V, A-C = 478V, B-C = 463V. It was then that I discovered there was a phase voltage imbalance coming from the town's substation.

Since it is a relatively new plant, the customer was the only one on the feeder from the substation, so no one else could notice any problem. After calling out the town's electrical contractor, it turns out that the C phase (single-phase) voltage regulator motor was seized and would not operate. It was stuck on 1 tap above neutral. The other tap changers were operating at several taps above neutral, which left a phase imbalance of a little better than 23V on B-C phase.

This voltage imbalance was only affecting this particular motor (using Y-Start, Delta-Run) and some of the electronic soft-starters. All the other motors in the plant were normal across-the-line Delta contactor motors and VFD driven motors, which did not seem to be affected by the voltage imbalance.

Following the replacement of the faulty tap changer, the problem has since disappeared.

__________________
All rights reserved. Lefts served only once.
Register to Reply
Register to Reply 15 comments