Long time lurker, first time poster, my location is United States.
One of our customers has had a puzzling problem with a piece of equipment.
The equipment was purchased, used, last year and since it was installed, has been operating well until recently. I am uncertain of the age of the equipment, but the control panel uses an Allen Bradley SLC 150, Logic Control equipment that has been obsolete for many years already, so this gives an indication of it's age.
The equipment is a decanter with a 30KW (40 HP) motor. It's nameplate is 230/460V, 49A, 3535 RPM, 60 Hz, 3 Ph. It has 12 motor leads.
All wire sizes are correct according to the NEC, and the control panel was wired according to the manufacturers drawings.
The motor is connected to the load using 8" OD drive pulley and 9" OD driven pulley, using a matched 3 belt set. The load is a high inertia decanter.
The electrical starting sequence is a typical "Y" start, Delta run configuration, with a timer to control the "Y" start time.
We were called in when the motor would not start up properly.
When the system is started, the main motor contactor closes, and the "Y" start contactor closes. The motor draws approximately 70 Amps on all three phases, phase to phase voltage is approximately 460VAC on all three phases, but the motor will not rotate at all with the drive belts attached. If the drive belts are removed, the motor will "slowly" come up to speed, but in either case, the motor does not appear to have any appreciable start-up torque. After the designated "Y" start time, the configuration switches to Delta run, and the motor will start to rotate, but will trip off on over-current after a few seconds.
After inspection, all appears to be in good order with the panel feeders, and panel wiring. The motor contactors were disassembled and inspected and appear to be in good order, with suprisingly little wear on the contacts. Contactor coils all measure good resistances.
We tested the motor on-site and all motor terminations appear good, a motor megger test was performed both from the panel and locally at the motor termination box, which showed good. Winding resistance tests also showed good both from the panel and locally. Running out of ideas, we began to suspect that perhaps the rotor shorting bars had open-circuited.
The motor was removed and brought to a local repair/rewind shop that we have used before with good results. The technicians disassembled the motor and other than a drive end bearing that they say made a little growling and was was replaced, have tested the motor as follows:
Visual inspections of stator and rotor are good,
Hi-pot tests are good,
Motor winding resistance tests are good,
Motor rotor magnetic tests show no problems with the rotor shorting bars of the squirrel-cage rotor,
Motor has been connected in their shop and run in a high-voltage Delta configuration, with no load, and they say the performance is acceptable.
The repair shop has improvised a low-voltage torque test. They used approximately 120VAC as a test voltage from an 3 phase auto-transformer, and achieved approximately 16 lb-ft, in a stalled rotor test. Assuming torque is linear, they say this would calculate out to approximately 64 lb-ft of torque. The motor torque calculated from horsepower is approximately 60 lb-ft. According to Stallcups's Generator, Transformer, Motor and Compressor book, the auto-transformer configuration they used will give the same effect as full-voltage starting, with good torque characteristic, which would explain their results.
After the repair shop's inspection, the motor was re-installed and re-tested with the same previous results, almost zero starting torque in "Y" start configuration.
We then reconnected the motor using a high-voltage Delta configuration to a Variable Frequency Drive. The motor is now functioning correctly and does not seem to suffer any lack of torque on start-up with the VFD driving it.
My question is, why would the motor all of a sudden display no appreciable torque with a "Y" start, while all windings test out normal both on-site and at the repair/rewind shop, but then operate normally when connected to a VFD in Delta configuration?
"Almost" Good Answers: