Hi,
This day be a good one for everybody !
We've procured the AC power source(Non standard -assembled product)
In that we found an o/p voltage variation w.r.to input supply.
Initially,Meter is connected to (230v AC input) & the power source is adjusted to 300v & the same is verified against the HP multimeter which indicates as 298v.
Then we change the AC i/p supply to DC supply by connecting on line UPS(220V) & as like above power source is adjusted to 300V & it check against multimeter & this found to be 288v.
Now I need your clarification for the below..
1. Is that much variation(10v) will be measure b/w the input supplies AC & DC?
2. What is the basic principle behind this ?
Need your assistance to come out from the confusion.
[Information is knowledge]
Re: AC power source - Output voltage variation
10/24/2008 3:55 AM
This is about what you'd expect if your device contains just a variable ratio autotransformer (Variac). Without knowing more about what's inside, can't say much more about it.
Good Answers: 15
Re: AC Power Source - Output Voltage Variation
10/25/2008 8:31 AM
Hi,
If I understand your post correctly you are saying that the output of your UPS is 300V when it has an A.C. input but that it only has 288V when supplied by the battery?
If so then the probability is that your meter is not true RMS reading and that the inverted waveform is not sinusoidal.
A typical inverter technique is to produce a width modulated pulse output with a peak of +/- 300V when the batteries are at full charge (2.4V/cell typ assuming lead acid) with the width of the pulse being regulated to give 230Vrms. As the battery voltage falls to 2V/cell the peak voltage will drop by 20% also and the width of the pulses is increased to maintain the 230Vrms. The limit is reached when the pulse width leaves no dwell time at 0V thus producing a square wave. At this point the inverter will usually shut down to protect the batteries from over-discharge.
This system works well for I.T. applications as most of the loads are SMPS units anyway. As the first stage of the SMPS rectifies the input it doesn't usually care about the supply waveform.
Check with a TRMS meter and/ or an oscillascope. See sketch below.
Hope this helps
Chas
10/28/2008 4:31 AM
Hi chas,
Thanx for your information.
Could you give me the RMS factor by how much DC voltage varies with respect to the AC voltage.
This will be useful for me to do calculation ...
Hari
Good Answers: 15
10/28/2008 12:13 PM
Hi Hari,
The basis of this is that the peak voltage of the pulse = Peak voltage of a 230Vrms sine (325V^) and the width is calculated from that. The minimum voltage will be 230V (equivalent to typically 20V for a 24V battery) which will be a square wave, at which point the pulse width is at max.
I believe that you will find that at the max peak you will get a nearer to true value than when the waveform is square.
The actual peak values depend on the manufacturer of the equipment and their transformer design. The variation from nominal of +/-20% approx will also change if the batteries are of a chemistry other than lead acid.
Kind regards
Chas