Anonymous Poster

Genaration and Transmission

10/24/2008 3:13 AM

Could any one please explain as to how to work out the follwings through simple calculations (thumb-rules) :

1) Kwh generation of 1 MW Power Plant - (What PLF (Plant Load Factor) along with the average hours per day operation of the Plant should normally be considered for the purpose)

2) Transmission Voltage to evacuate the genearted power in Point 1) above (i.e. what should be ideal KVA of the transmission line to tramsmit this generated power over a distance of 100 KM for example and how do we decide that?)

Regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#1

Re: Genaration and Transmission

10/25/2008 1:44 AM

The Plant Load factor is very difficult to predict - We have plants with Load factors as high as 90+ to the ones with PLF less that 60%

It all depends on the plant machinery reliability, maintainability, conditi, load pattern (whether the energy generated can be evacuated) etc.

PLF is calculated over a time period (monthly, annual etc) and are not instantaneous. No thumb rule for this.

Other part is -

generated units = 1000 x 24 x MW x PLF x no of days(PLF calc duration) units.

For transmission - KVA

Take average PF = 0.8 and you get

1MW/0.8 MVA = 1.25 MVA

- you have to design the transmission line on full capacity and not on PLFs

the KV is for you to decide based on the grid voltage, and other economics, lower voltage = more line loss, more copper in lines.

Higher Voltage = More transformer (step up, step down) and insulation costs

Thumb rule may not apply. But all designs is on the generation capacity and not on PLF. We design the generation capacity on PLF so that customer get un interrupted supply.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply Score 1 for Good Answer
Member

Join Date: Feb 2008
Posts: 5
#2
In reply to #1

Re: Genaration and Transmission

10/25/2008 2:59 AM

Thanks Sb for the valuable inputs. It's a great help.

Regards

Reply