Power factor Correction

10/27/2008 2:46 PM

Our building in the USA has 277/480 service. Most of the load is on transformers because it is 120 volt fluorescent lighting. Does power factor correction go before the transformers or after to be most effective? Is the correction needed something I can figure with small portable equipment or do we need more extensive testing to determine what is needed. Also, does the same apply to the 277V HID lights in the warehouse areas? Thanks -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: Power factor Correction

10/27/2008 5:06 PM

Hey CB,

If most of your load is from your lighting circuits, you may want to consider the age of the ballasts. If they are new electronic ballasts, you probably don't have much of a power factor issue.

If instead, they are the old klunky (technical term for big and heavy) cheap magnetic ballasts then there could be a slight improvement with the addition of a capacitor at the actual ballast. You might want to start by looking at the utility bill for your electrical consumption because your average power factor should be on it.

You can address the power factor on either side of the transformer but eventually the ballasts will be replaced and then you won't need PF correction. Some of the old magnetic ballasts included capacitors in their design. There is a good chance that you only have two makes (models/types) of ballasts to consider. Check it out and get back to us!

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Anonymous Poster
#2

Re: Power factor Correction

10/27/2008 9:42 PM

I consider the transformer is big enough as it is for the entire building . I want to inform u that if power factor is low that means more current will be flowing through all the cables , switches , main switches, transformers and this is going to continue upto the power generation source. Under stand that with low P.F. It will be overloading of equipments or underutilisation of equipment. It is important to note that overall power drawn is going to be same in any case.

The best way to correct P.F. is to attach capacitor with the light Or any other equipment which uses copper winding and produces magnet ( like electric motors , etc.)

After adding capacitors with the lamp u should put automatic P.F. controller on the output ot the stepdown transformer. YOU are also recomended to attach one capacitor of suitable value to the input of transformer ( this will take care of low P.F. due to transformer).

In case more details are required than mail me at narwal_sunil@yahoo.co.in

Register to Reply
Anonymous Poster
#3

Re: Power factor Correction

10/28/2008 9:21 AM

You can use a a portable load recorder to take measurements to size your power factor correction capacitor.

Just a few things to keep in mind:

Your load changes daily , seasonally. The automactically switched banks work good becuause they can switch in and out the correct amount of VARS as required without overcorrecting.

I would think you would want the PF Correction as close to the equipment that is causing the problem. You may want more than one bank.

I have monitored circuits with the Caps in and out of the circuit. Like you other guest notes, The KW does not change. Your kVA, and current draw decrease. It was kind of a waste for my client because he thought he was going to save $$ on his utility bill. It turned out the utility PF penalty was minimal.

Register to Reply
Member

Join Date: Oct 2008
Posts: 5
#4
In reply to #3

Re: Power factor Correction

10/28/2008 9:54 AM

Your statement is a little backwards. KVA is the apparent power (rating of the transformer). KW is the actual power consumed (true power consumption). Power factor is nothing more than the ratio of true power to apparent power or KW/KVA. EX... If you have a 30 KVA transformer and a wattmeter reading 24 KW of consumed power...you have a power factor of 24/30= .8 = 80% Power Factor

Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#6
In reply to #4

Re: Power factor Correction

11/05/2008 9:25 AM

Hey HollaIFyaHEMI , what if he had a 100kVa transformer? Probably would make more sense if you had said "if you measure 30 kVa and 24 kW . . .otherwise a world full of trusting individuals on this site might get their math very confused based on transformer size and not measured values.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#5

Re: Power factor Correction

10/29/2008 12:16 AM

If the pf correction is done at the inlet of the transformer,

the line draws the optimim current , however within the transformer both the zero phase and the reactive current flows, losses increased.

If on the secondary side, the reactive is taken care of by the transformer and transformer losses are minimized but the line current will be including the transformer reactance.

The second case is likely to be much smaller., also putting capacitabnces in the secondary may be cheaper (lower voltage)

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Register to Reply 6 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); CJMcGill (1); HollaIFyaHEMI (1); NotUrOrdinaryJoe (1); sb (1)