Why shoud i use busbar for Power Distribution Panel?

11/02/2008 4:56 AM

Hello All,

I need to design power ditribution Panel using 30 mcb's. Main MCCB is 100A. Should i use busbar or not for distribute from MCCB to each MCB?

I still dont understand what is the purpose for using busbar?

regrads,

imufthi

Register to Reply
Pathfinder Tags: Busbar
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Nov 2008
Location: S.E. Asia
Posts: 91
Good Answers: 1
#1

Re: Why shoud i use busbar for Power Distribution Panel?

11/02/2008 7:39 AM

Most of these types of Distribution Boards are readily available "off the shelf" items. I wouldn't bother with designing one. However, the question about busbar versus cable is simple. If the "prospective fault current" of the supply to the Distribution Board is significant (>10kA), busbar would be prescribed to avoid the derating of the cable even though 10kA may seem small. Cables can't handle fault current in the same way that busbars can. Generally, busbar is rigid & can therefore better cope with the thermal & dynamic stresses created under "fault" conditions. Insulated busbar may have a small temperature rise problem (some derating may be needed) but will allow for a more compact design.

__________________
"If you try to keep a leg each side of a barbed-wire fence, you'll do yourself a mischief." - Joh Bjelke-Petersen.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#2

Re: Why shoud i use busbar for Power Distribution Panel?

11/03/2008 7:38 AM

Hello

By using busbar, in case you need to remove one of the branch mcb, you can do it and switch on the main MCCB again. If the branch mcbs are connected by wires, this removing one branch is difficult or unsafe.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Guru

Join Date: Aug 2006
Posts: 4484
Good Answers: 246
#3

Re: Why shoud i use busbar for Power Distribution Panel?

11/03/2008 11:27 AM

Yes, use a busbar. One reason is simply practicality: panels are available for small systems like this and they are based on a busbar, for the reasons mentioned by others and for the simple fact that the busbar is a simple connection point. In the US, a panel like this is available at your local Home Depot at a price so low as to preclude any thoughts of custom designing and building one. The breakers snap right in, it meets code, etc. etc. etc.

__________________
There is more to life than just eating mice.
Register to Reply
Participant

Join Date: Nov 2008
Posts: 3
#4

Re: Why shoud i use busbar for Power Distribution Panel?

11/05/2008 9:56 PM

Hi All,

Thank you for all your answer.

regards,

Register to Reply
Register to Reply 4 comments