Can somebody please explain me the difference Between them.All I know is that ,Contactor is a switching device and CB is a protecting device.The concept of latching and holding coil is also not clear to me.Please explain it to me
Good Answers: 143
Re: Difference Between Contactor and Circuit Breaker
11/02/2008 10:58 AM
At a very practical level, a contactor is meant to be operated by a means other than the electricity the contacts carry; thus, a contactor can have pitted or dirty points and still function. A contactor will usually operate for thousands and thousands of times.
A circuit breaker is meant to be operated by the electricity the contacts carry; thus an opening usually means at high current with resulting damage to point surfaces. A circuit breaker that has opened several times, or that has been misused as a switch, is likely to not function at spec level.
A latching relay (or contactor) is one in which one set of normally open contacts is put in series with the coil. Thus, any interruption in the coil current causes the coil to release that NO contact, requiring a manual (usually) reset.
You can get fancier with these circuits, but I think that's the basic ideas you need.
02/15/2010 1:53 AM
The main difference is that a circuit breaker is designed to interrupt fault currents while a contactor is not. There are other differences in terms of cost, opening time, etc, which are of secondary importance.
05/08/2010 8:42 AM
i need a comprehensive circuit diagram,and a picturial view of a contactor.including its practical connection.