Hi friends,
I would like to know how to calculate the cooling requred for electrical panels.What is the calculation using for it.?
United States - Member - New Member Technical Fields - Technical Writing - New Member Popular Science - Weaponology - Organizer Hobbies - Target Shooting - New Member Engineering Fields - Nuclear Engineering - New Member
Re: Cubicle Cooling
11/10/2008 8:36 AM
Do you have electrical panels in cubicles? The title to this thread is "Cubicle Cooling", but I don't see any mention of office partitions in the question itself.
Re: Cubicle Cooling
11/10/2008 8:52 AM
Dear Mr.Moose,
Industrial cubicle system is actually metal cubicle comprising a triangle profile structure,welded closed at the top and bottom frame,with removable screw in vertical profiles to give the unit strength and versatility.
Application: Industrial cubiclefor PC,MCC Panels,MDB's.
Re: Cubicle Cooling
11/10/2008 10:17 AM
Outstanding! Thanks for the additional details, prasobh83. This is not a question I'm able to answer, but hopefully the extra information will enable other CR4ers to help you.
Regards,
Moose
Re: Cubicle Cooling
11/11/2008 2:40 AM
Hi,
Panels for industries have an ambient temp at which they should work. This is pre-defined during design stage. Their are lovers provided for ventilation to cool the panel. Some times small fans are installed to extract the heat.
If the temperature of panel is high, it may affect the equipments/instruments inside it. You can place a portable fan near the panel to provide cooling. But if you require extra cooling - you need to provide it through a duct connected to an AHU so that some chilled air (moisture free) can come in contact with the panel and provide cooling.
regards,
Ashish
Ashish Gupta
Good Answers: 15
Re: Cubicle Cooling
11/10/2008 11:02 PM
In each part of equipment your installing inside, do you have its Temperature rise above Ambient caculations/results?
As its ambient temperature will be the insides of the enclosure, then the Thermal resistance from inside to outside will be the thermal conductivity (DegC(F)/W)
If your running a "non-ventilated" enclosure, you'll have to design a system which will remove the generated heat inside the box, and transfer it to the outside environment.
This has been done previously using Heat-pipe technology through the sides of the enclosure with the heat fins on the outside and fan force inside for circulation
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake
Re: Cubicle Cooling
11/11/2008 2:35 AM
What you need to establish the Ambient temp where this panel is sited.
Find out what is the heat load coming form within the panel.
Know the size LxBxH of the panel
What material it is made of steel sheet, aluminium, stainless/steel...
Is this panel sited in the outdoor or indoor
Follow this link http://www.pfannenbergusa.com/software/download-sizing-software.html & download the free software that will precisely tell you what is the cooling capacity
Good luck,
Philip Koh
Re: Cubicle Cooling
11/12/2008 1:31 AM
Snaiktails has answered your question very well.
To add to it, you are in a better position to assess the heat load that is to be dissipated. Every cubicle has different kinds of switchgears going inside from push buttons, drives, contactors, relays and even transformers. Each of these will dissipate certain amount of heat which is given in to the cabinet. The walls of cabinet dissipate some amount of heat to ambient and if it is not sufficient, you involve a fan (with filters) to draw fresh air from ambient to remove the heat. For higher heat removal and depending on other criteria like quality of fresh air, you may have to choose from Heat pipe heat exchangers or even vortex coolers (requires compressed air). all said and written, except in vortex coolers, ambient plays a major role and the T achievable depends on the thermal resistance that you are ultimately able to achieve as is already mentioned by Snaiktails. visit www.capri.co.in
B +ve
Re: Cubicle Cooling
11/15/2008 3:05 AM
I'm working on a project which require IP65 Enclosures, thats where you can't use fans for removing the heat, but heat load is the most important data you need in order to size the enclosure cooler, some drives like soft starter and inverter generate a lot of heat , you can check from RITTAL website for enclosure Refregerant Air Conditioner, they do have many models for you to choose.
http://www.rittal.com/products/katalog.asp?FirstNav=1&ViewAt=3&lang=GB&Dom=com
but let me warn you, it is not going to be cheap. be prepared for it.
William Tan
There are no Mistakes , Only Lessons.
Re: Cubicle Cooling
11/15/2008 6:54 AM
Thank you for your help.I am using HIMEL Enclosures.They also have cooling units for panels.But for MCC's and all if we go for cooling units it will not be a cost effective solution.An IP of 55 range will do for me.
Re: Cubicle Cooling
10/09/2014 10:01 AM
Pfannenberg (www.pfannenbergusa.com) offers a variety of solutions for cooling electrical cabinets. Depending on ambient temperature and dust in the enviroment there are different closed and open loop solutions.
Re: Cubicle Cooling
11/15/2008 9:02 PM
Oh, I see, you only want the calculation right? Try this one :
To Calculate the TOTAL HEAT LOAD for your panel
Total Heat Load = Heat Dissipated within the enclosure + Heat Transfered from outside into the enclosure
1. Determine the approx. watt of heat generated within the enclosure
watts x 3.41 = (internal heat load ) Btu/hr
2. calculate outside heat transfer:
a. Determine the area in ft sq exposed to the air, ignoring the top of the enclosure
b. Determine the temp diff between maximum surrounding temp and desired internal temp. Then, use the temp conversion table below to determine the Btu/hr/ft sq for that differential, multiply the cabinet surface area times Btu/hr/ft sq, that will provide you the value for external heat transfer in Btu/hr
3. Add the internal and external heat load for TOTAL HEAT LOAD
Temperature Conversion Table
(Temp. Diff ) Btu/hr/ft sq
(5 ) 1.5
(10) 3.3
(15) 5.1
(20) 7.1
(25 ) 9.1
(30 ) 11.3
(35) 13.8
(40) 16.2