Earthing 336-kV Lightning Arrestor

11/13/2008 9:10 AM

Hai everybody. Please clarify me whether it is advisable to connect the 336kV lightning arrestors of power station to the stand-alone earth pit. Or is there any advantage if the earth pit is linked to the station earth grid which is common to the several system of voltages. It is observed that the views of authors of different text books when searched in the web are not the same. The statute like BIS is also not very particular about the type of earthing, even though it is indicated in a typical earthing lay out diagram as inter-connected to the earth grid. The doubt is that as the combined resistance of an earth grid is far lesser than the stand alone earth pit, then what is the need of an earth pit. Also what is the effect of travelling waves in the event of discharge of a lightning stroke in to the earth grid which can cause high frequency oscillation. The purpose of the earthing the lightning arrestor is to discharge the surges in to the earth with out causing raise of dangerously high potentials in the vicinity of the lightning arrestors and to dissipate the power in to the soil, it seems that a stand alone earth pit is preferable than connecting to an earth grid.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#1

Re: Earthing 336-kV Lightning Arrestor

11/13/2008 8:37 PM

Dear all,

The lightning arrestor earth must be directory connected to the earth of the equipment which is protected by the arrestor. For instance, if a transformer is protected by the lighting arrestor, the lightning arrestor earth must be connected to the transformer earth with an earthing conductor as short and straight as possible.

Transformer earth is probably connected to the entire earthing system of the plant, so eventually, earthing of lightning arrestor is also connected to the earth system.

You may have additional earth pit as you want to reduce the total earth electrode resistance.

When the lightning arrestor fires, potential of earthing system raise. Potential of all earthed components raise at the same time. So, there will be less potential differences among earthed components.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia