construction joints in raft foundation

11/17/2008 4:56 AM

do we need to provide shear links in raft construction joints when the raft thikness is is more than 1m ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Member

Join Date: May 2008
Location: Middle East
Posts: 9
#1

Re: construction joints in raft foundation

11/22/2008 11:19 PM

Yes, You need to provide a joint with KEY and rebars crossing the joint. The spacing of joint depends on the thickness and plan size of the raft. Also, per good detailing practice, provide a waterstop across the key to avoid moisture ingress.

Akhtar Naviwala

Register to Reply
Member

Join Date: Aug 2008
Posts: 7
#2

Re: construction joints in raft foundation

12/22/2008 5:42 AM

you have to provide key construction joint and reinforcement have to continue whether with overlap or couplers system,key joint should be roughened and water stop bars to be provided.location of construction joint to be agreed from with the designer of the raft to determine where are the best locations to avoid the max moments and shear forces.

co-ordination with the MEP contractor should be.

Register to Reply