e-stops

11/17/2008 4:27 PM

have a 2510 class square D manual motor starter wired directly to the motor. is there any way to wire in a e-stop? this is 230v 3-phase.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: e-stops

11/17/2008 7:35 PM

Interposing relay?

Register to Reply
Active Contributor

Join Date: Jun 2008
Location: Dartford, kent , England
Posts: 11
Good Answers: 1
#2

Re: e-stops

11/18/2008 4:45 AM

From googling it i would say you can not add an Estop to the starter itself... looks like just a main supply feed in , manaul contactor and the output feed to the motor.

you need some control equipment / relays either in a seprate MCC or replace the starter with one suitiable for emergancy stop system.

Here in the UK all Motors should have emerency stop buttons installed as per the PEWER regs.

Is the Starter in a hazadous area? looks like its is made for hazadous area's if i have found the correct starter on google?

__________________
Raise to the challange and do it safely
Register to Reply
Associate
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2007
Location: India
Posts: 42
Good Answers: 3
#3

Re: e-stops

11/18/2008 8:49 AM

Dear Sir,

E-Stop (EMERGENCY STOP-Push button) shall be wired in series with control circuit energising the main motor contactor.The E-PB can be press to lock and key to release type.The E-PB station will be kept near the motor to stop the motor in the case of emergency situation.Hence the name of the PB as E-stop.

V.Ambarani

__________________
Best Regards
Register to Reply
Active Contributor

Join Date: Jul 2007
Location: Houston, TX
Posts: 23
#4

Re: e-stops

11/18/2008 3:26 PM

Break the connection between the stop switch and the starter relay coil and insert the E-Stop switch in series with this circuit. The E-Stop switch must be a manual push to actuate pull to reset and not a spring return type. Check with your Square D dealer. You may want to replace your manual switches with momentary switches and add an auxiliary contact keep the coil energised to address some potential safety issues.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#5
In reply to #4

Re: e-stops

11/19/2008 12:01 AM

Friend,

The starter he referred to does not have switches; the buttons do a mechanical operation. Like a circuit breaker, with load sensing which unlatches it so it turns off.

--JMM