Delta to star starter

11/29/2008 11:05 AM

Hi friends,

One 400V, 30KW,59A, delta connected squirrel cage IM used for vibro screens. If we connect it in star it is working normal and consumes less power than delta. But since starting torque is low it trips sometimes. So can we start the motor in delta and run it in star ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Delta to star starter

11/30/2008 12:02 AM

Motor consumed power is a factor of two basic elements; load (shaft) power and losses. Any motor, no matter how connected, will only consume the load power that the load requires. So the only thing you are really changing by connecting it in star is the amount of losses. The losses break down into several sub groups, such as magnetic (iron hysteresis), copper (resistance or IR), friction and windage. The only parts of these losses that are affected by connecting it in star are the copper and iron losses, which make up about 60% of the total losses. When a motor that was designed to be connected in delta is connected in star, the effective voltage across the windings is lower by 58%. It consumes slightly less power because the iron losses are lower as a result of the lower magnetizing energy and the current is lower, so the IR losses drop as well.

But the current is lower only because it can be, and that's just because you have essentially a smaller motor when connected in star. Torque is related to the square of the voltage, so at 58% voltage, you get .58 x .58 or .33 or 1/3 of the normal torque. 1/3 torque and the same speed will equal a lower mecahnical HP (kW) output; 1/3 that of what it was originally designed to put out. If your load is such that it can continue to do the necessary work with 1/3 of the installed motor power capacity, then someone has grossly oversized that motor in the first place. The only caveat is if the over sizing was necessary to get enough starting torque to overcome inertia or friction. If that is the case, then by all means, you can run it in star after getting it to full speed. But remember, you will no longer have a 30kW motor, you will have a 10kW motor. If your operating load increases to require more than 10kW mechanically, that motor will stall.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2008
Location: India
Posts: 91
Good Answers: 6
#4
In reply to #1

Re: Delta to star starter

12/02/2008 9:29 AM

Dear JRaef,

Thank you.

you will no longer have a 30kW motor, you will have a 10kW motor

I dont agree with this. In star 30kw motor would become 30/1.732=17.3kw.

Power= 1.732*VL*IL*P.F

The motor rating is decided by the maximum current flow through each winding.

In star IL=Ip, IL would be 1/1.732 times of delta. So the rated power would become 1/1.732 times.

But the starting torque of star would be 1/3 times the starting torque of delta.This is correct.

Kindly advise if i am wrong.

Register to Reply
Anonymous Poster
#2

Re: Delta to star starter

11/30/2008 3:04 AM

This is a mind bender. Delta is impedence parallel with respect to time and electrical degrees of rotation. Star is impedence series with respect to time and electrical degrees of rotation. At any instance of time a delta circuit splits current through two windings and exits through the two remaining legs and (T leads). At any instance of time a star circuit chooses one impedance path through the incoming path (one motor winding) and exits two legs (motor windings &T leads) in series with it through the two remaining legs. It took me years to see this. I hope I am explaining it well enough for you to understand. You may also note a star connected motor doesn't develop the same torque / horsepower as a delta connected motor. The difference is insignificant, but notable.

Register to Reply Score 1 for Good Answer
Commentator
India - Member - Electrical Energy

Join Date: May 2007
Location: Tamilnadu
Posts: 57
#3

Re: Delta to star starter

11/30/2008 4:14 AM

No. The motor windings should not be connected to delta at the time of starting.The rated voltage is applied across each winding in delta position and the high starting current may damage the windings.

Register to Reply
Commentator

Join Date: Nov 2008
Location: S.E. Asia
Posts: 91
Good Answers: 1
#5
In reply to #3

Re: Delta to star starter

12/04/2008 10:59 AM

Haven't you heard of D.O.L. starting?

If what you say is true, millions of motors around the would are having their windings damaged as we speak.

In the meantime & disregarding the appropriate size of the motor, it seems to me that this particular motor could be started in "star" & then run in "delta"...a typical scenario.

What is your main concern? Power consumption?

__________________
"If you try to keep a leg each side of a barbed-wire fence, you'll do yourself a mischief." - Joh Bjelke-Petersen.
Register to Reply
Commentator

Join Date: Sep 2008
Location: India
Posts: 91
Good Answers: 6
#6
In reply to #5

Re: Delta to star starter

12/04/2008 12:21 PM

Dear elkangorito,

Yes, my concern is power consumption.DOL starter is currently used for this motor.This motor is delta connected. I took trail in star observed power saving. It is working satisfactorily in star at running. The main problem is it sometimes, unable to provide the required starting torque.That is why i am thinking about Delta/ star starter.i.e. Starting it in delta(to get higher starting torque), and running in star(to save power).

Thank you,

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); elkangorito (1); G.Swaminathan (1); JRaef (1); Lspraba (2)