Power factor

12/03/2008 5:32 AM

Dear All,

Please explain me what would be consequences in synchronous generator if the power factor is maintained unity?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Power factor

12/04/2008 8:28 AM

Only good stuff. The sun will come up on time, farmers will get all the rain they need, global warming will come to an end, sunspots will all disappear, world peace...

In short a power factor of 1 is exactly what you want (unless you are using some off the wall weird induction generator which requires VARS from the system for excitation)

Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Power factor

12/04/2008 8:57 AM

Well , maybe 0.8 pf is what you want for best generator stability.

At nity pf you are rigt on the margin where underexciattion and system disturbances can cause pole slippage.

Register to Reply
Anonymous Poster
#3
In reply to #2

Re: Power factor

12/05/2008 1:25 PM

at 1pf, KW=KVA, hence less copper losses in the generator, as pf decreases from 1 to 0.8, the current increases proportionally, and the losses increase in the genset, see any genset manufactures efficiency curvers...

Register to Reply
Associate
India - Member - New Member

Join Date: Mar 2007
Location: India Bangalore
Posts: 40
#4
In reply to #1

Re: Power factor

12/17/2008 4:46 AM

But due to Power factor corrected power supplies of Information technology equipments has created Power factor towards unity or leading also. We have seen UPS connected to these loads working on Leading power factor. We had to de-rate the UPS and load ( Because Ours are legacy UPS manufactured 4 years back for 0.8pf and filter is combination of harmonic filter and power factor improvement)

Our DG power factor is 0.9, because of high chiller and induction motor. But I would see unity power factor in near future. I really do not know how Generator manufacturers will align for this change as they are designed for 0.8pf lag.