12/10/2008 11:54 AM
How a dp transmitter calibrated in few 1000mmH20 can able to display flow of 20-50 kg/hr or pressure transmitter can able to show 100kg pressure.
what actually is the relation between the calibration range and display unit...
and why we select mmH20 only why not we calibrate directly on kg or bar
Re: Calibration basic
12/10/2008 1:22 PM
It's because a dp transmitter does not measure flow, it measures delta-pressure in a pressure-loss type flowmeter. You're making some confusion: delta-pressure is pressure measurement, may be measured in psi, bar, mmH2O, mmHg, etc. kg/hr is mass flow, as is ppm. kg is unit for mass. Pressure transmitters do not measure mass. You may have meant 100 kg/sq cm or so.
The flowmeter then is designed to have a known dp for a given flow, and that's how we measure it. Mainly in compressive flows, it will vary with pressure and temperature, thus, you'll need a kind of flow computer to show you the flow directly. And there's your calibrated indication in flow.
Its in mmH2O because the less delta-p, the better for the process - less energy cost. But still need a good transmitter to assure consistent measurement. You could still measure it in bar or psi, but the measured value would be so small that would be hard to deal with.
Humm... suspicious you are...