about neutral ct

12/11/2008 11:33 AM

just i want to know about neutral ct

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: about neutral ct

12/11/2008 12:20 PM

Are you asking about a current transformer on a neutral line?

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#2

Re: about neutral ct

12/11/2008 6:42 PM

The usual reason to put a CT on a neutral line is to find out what the neutral current is in the circuit. In a three phase circuit, if all of the three phases are perfectly in balance, there will be no current in the neutral line. There will be more neutral current as the imbalance between the phases increases. There will also be neutral current in a three phase circuit if there is a ground fault on one of the phase conductors.

In generator service the neutral current CT may feed into a protective relay to shut down the generator if there is too much neutral current.

I have seen a neutral CT used to find leakage current in a single phase circuit. If the current in the neutral line was not equal to the current from the CT on the hot conductor, there is a ground fault on that circuit and some current is returning to the feeder panel through the ground conductor.

I hope this made sense as you didn't give a lot of background.

Live a joyous life!
TT3

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Anonymous Poster
#3

Re: about neutral ct

12/13/2008 2:14 AM

The CT on a neutral is used to measure the earth fault current, this is a standard protection system (51N).

Sometimes it is coupled with three current transformer on theother side of the generatoe or transformer this is named restricted earth fault, because it is protecting the equipment.

Register to Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#4

Re: about neutral ct

12/14/2008 8:52 AM

There is usually only 1 reason to measure the Amperage on a neutral; to monitor imbalance or ground fault. This is because the neutral serves as the unbalanced load current conductor. when there is a current on the neutral it is a result of either an imbalance between the 3 phase conductors or a ground fault.

__________________
Tell 'em what they need to hear; not what they want to hear!