Anonymous Poster

Power Factor

12/12/2008 11:53 AM

I have a 3 phase wye connected motor. I can measure rms current in each phase and rms voltage line-to-line. I cannot measure line to neutral rms voltage but can calculate with sqrt of 3.

With only the above information, can you calculate power factor?

Vrms (line to line) * Irms (line to line) = KVA apparent power ???

how to calculate KVAR(reactive)? KW(actual)?

what else do I need to measure (I have no scope to see phase shift)

thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#1

Re: power factor

12/12/2008 12:07 PM

How curious, the phase difference between the current and voltage is exactly what you need. Perhaps some one can explain a way to measure the phase difference from what you already know but I do not know how myself.

????
TT3

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Reply
Anonymous Poster
#2

Re: Power Factor

12/12/2008 2:29 PM

seems I need to buy 2 wattmeters, no wye neutral pullout

I was hoping there might be some trick to obtaining power factor or at least get a good estimate based on limited information

Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#3

Re: Power Factor

12/12/2008 3:48 PM

No calculation exists for only those two parameters that = PF.

Some standard assumptions exist, but are estimates about the average PF of certain situations (usually around 300 lag).

If this is not a theoretical query and you want to make the calculation less frequently than would indicate buying 2 kW meters, then this link might be helpful.

Adding the phase angle to your information will allow you to calculate all of the values you inquired about.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#4

Re: Power Factor

12/12/2008 11:21 PM

guest: you do not mention the line to line voltage, is it? 380/220, or 480/277, why would want to measure neutral voltage to line voltage? watt meter rule is N minus lines, that is 3 phase 3 wire, 2 watt meters needed 3 phase 4 wire , 3 watt meters needed, this will give you the watts used. next you need a rms reading volt meter and rms, iron vane amp Reading meter, volts times amps give you volt/amps or KVA if measured against a Resistance heater they should be the same. if inductive load, reading the kva against the KW there would be a difference. perry

Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#5

Re: Power Factor

12/13/2008 7:20 AM
DEAR READER,

POWER FACTOR = REAL POWER ( KW) / APPARANT POWER ( KVA )

= (KWH2 - KWH1 ) / TIME

-------------------

1.732 * V LINE * I LINE

KWH2 / KWH1 ARE ENERGY METER READINGS .

BUT, NOW IT IS SIMPLE TO MEASURE THE PF DIRECTLY FROM LOAD MANAGERS AVAILABLE.

__________________
Exploring the Science of Electricity
Reply Score 1 for Off Topic
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#6
In reply to #5

Re: Power Factor

12/13/2008 2:34 PM

Where as "POWER FACTOR = REAL POWER ( KW) / APPARANT POWER ( KVA )" , this question came without a way to measure kW.

As for "= (KWH2 - KWH1 ) / TIME" , again he is able only to measure Line volts and Line amps. Besides, this equation makes no logical sense to me and I've metered and taught metering for a long time. You would have to explain the circumstances of these measurements, for instance is one measuring a purely resistive load of the same amps etc.

Also if "KWH2 / KWH1 ARE ENERGY METER READINGS", how do readings alone offer any useful detail? Are they readings of the same meter at different times? Are they a kWh meter and a kWh meter wired to measure kVARh?

Also "1.732 * V LINE * I LINE" is the formula for 3 phase VA. How can he use this without the phase angle, VAR or kW to calculate PF?

In brief, and not to be critical, can you clarify some of your references for the questioner please.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Reply
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#9
In reply to #6

Re: Power Factor

12/15/2008 2:55 PM

By kWh1 and kWh2 are the values read from the same meter at 2 different times. Making the difference of real energies (kWh) and dividing this difference by the time difference (t), it results the real (active) power (kW).

From the other readings (A and V) the apparent power can be determined, which, in turn, allows the calculation of the power factor as the ratio between real (kW) and apparent power (kVA).

This procedure allows the calculation of only an average power factor, in case the measured values of voltages and currents are also average values recorded along the same time interval. Otherwise mixing instantaneous measured values (A,V) with average values (kW) may lead to significant errors.

To determinate the power factor and thus reactive and apparent power with only current and voltage measurements is not possible.

__________________
Scientes et audaces fortuna juvat !
Reply
Anonymous Poster
#7

Re: Power Factor

12/15/2008 9:28 AM

thank you all for your inputs and thoughts,

expected little hope in calculation/estimating PF with such limited information and instrumentation on a 200 VAC line-to-line 400 Hz

I had always prefer to pull out the wye neutral and ground it for safety but as suggested I would need 3 wattmeters

Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#8
In reply to #7

Re: Power Factor

12/15/2008 12:09 PM

400 hz? Where do you live? :=)

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Reply