asking about the impedance of transformator

12/13/2008 5:08 AM

hi...

i'd like to ask about the impedance of transformator (in %). these are the specification of the transformator :

50 kVA, 100 kVA, 150 kVA, 160 kVA, 200 kVA and 250 KVA. all off them have 220/380 volt.

does anybody can help me ??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#1

Re: asking about the impedance of transformator

12/13/2008 6:53 AM
DEAR SIR,

IMPEDENCE OF TRANSFORMER IS BASICALLY THE DESIGNER'S CHOICE. ALL YOUR INTEREST IS TO RESTRICT THE FAULT LEVEL TO PERMISSIBLR LEVELS / POWER SUPPLY AUTHORITIES.

HIGHER THE IMPEDENCE, LOWER THE VOLTAGE REGULATION. BUT LOWER FAULT LEVELS , BUT MORE COPPER TURNS.

LOWER THE IMPEDENCE, HIGHER SHORT CIRCUIT FAULT LEVELS / LESS COPPER REQUIRED.

GENERALLY, MINIMUM VALUE ASKED BY SUPPLY AUTHORITIES ARE 5% IMPEDENCE.

WITHIN IS / IEC TOLERANCES.

__________________
Exploring the Science of Electricity
Register to Reply
Active Contributor

Join Date: Oct 2007
Posts: 12
Good Answers: 1
#2

Re: asking about the impedance of transformator

12/14/2008 11:19 PM

HI

% IMPEDENCE = Vsc/Isc

For all these given rating transformer Kva rating is different but voltage is 220/380v,here you will have to do short circuit test of these tranformer,

short the 220voltage side terminal,Apply the voltage at 380v side xmer terminal start from Zero.Also measure the current at 220Voltage side short circuited terminal

Increase the voltage slowly till full load current flows at 220voltage side.

Measured the Short circuit voltage at that time it is your Vsc & Isc you can take as full load current at 220v side.

Each name plate of xmer can give the details of %z also.

any this is the test from that Manufacturer get %Impedence.

regards

SJ

Register to Reply
Power-User

Join Date: Dec 2007
Location: Chicago, IL, USSA
Posts: 141
Good Answers: 3
#3

Re: asking about the impedance of transformator

12/15/2008 10:21 AM

It depends on the transformer design, some transformers like Drive Isolation transformers are designed with a higher impedance to reduce distortion caused by VFD drives. You will need to check with the manufacture but 3%-4% is a typical value for impediance of a standard transformer.