Earthed Cables and Unearthed Cables

12/14/2008 4:11 AM

Friends i want to know something about 11KV cables.

I want to know the difference between earthed and unearthed 11KV cables.

I know that their is some differnece in voltage insulation and also they refer that earthed cable is require to earth on both end of cable and unearthed cable is require to earth only in one side. My questions are as following :-

1. what is insulation level(Phase to phase and phase to outside) for both type of cables?

2. why unearthed cable is not earthed on both side whenever earthed cable is require to earth on both side. What are the advatages of doing earthing on one side and on which side(sending or receiveing side) we have to earth. What happen if we will earth both side in unearthed cable. Is their any chance of false earth fault detect by relay if we will earth both side in unearthed cable.

3. Why armound of earthed cable is earth on both side. What are advantages? one side earthing means it is earthed but why on both side earthing is required?

i am waiting reply from all my friends. i know you all are master in your field. kindly give ansure.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#1

Re: Difference between earthed 11KV cables and unearthed 11KV cables

12/14/2008 2:20 PM

Hi Yogesh Gupta,

In HT electrical distribution,the systm can be earthed or un earthed.

This same subject was discussed for a thread that came up in CR4 on 04/01/2008 . Please read my reply which is quoted below and please read all the other replies . It is always better to check the previous threads on the same subject before putting up a new thread.

"The selection of earthed/unearthed cable will depend on your system. If your distribution system is earthed then you have to use cable manufactured for earthed system. (which the manufacturer specifies). If the system is unearthed then you need to use cable manufactured for un earthed system.The unearthed system requires high insulation level"

"

For earthed and un earthed XLPE cables, the IS 7098 part2 1985 does not give any difference in specification. The insulation level for cable for unearthed system has to be more. In simple statement the manufacturers states that 11 KV earthed cable is suitable for use in 6.6 KV unearthed system.The process of manufacture of cable is same. The size of cable will depend on current rating and voltage level.

what IS specifies and I quote below:

" b) Voltage Grade (Uo/U)

1) Earthed System - 1.9/3.3 kV, 3.8/6.6 kV, 6.35/11 kV, 12.7/22 kV and 19/33 kV.

2) Unearthed System - 3.3/3.3 kV and 11/11 kV.

Note 1 - Cables of 6.35/11 kV grade (earthed system) are suitable for use on 6.6/6.6 kV (unearthed system) also "

Hope this will clear your doubts

Register to Reply Score 1 for Good Answer
Associate

Join Date: Jan 2009
Posts: 44
#6
In reply to #1

Re: Difference between earthed 11KV cables and unearthed 11KV cables

10/14/2013 6:42 AM

Dear Abraham,

I have seen many discussion forums wherein this topic has been deliberated in detail. From your name I guess you are from India and perhaps from Kereal state. Assuming this to be valid, can you please tell me whether the 11 kV supply from KSEB or TNEB or from any other state electricity board should be considered as Earthed of UNearthed. I think that the EB sub-station might receiev power suply at 66 kV or 33kV, step it down to 11 kV for distribution. All purpose the step down Trfo at the EB S/S must be a Delta/ Delta configuration and there is no scope for earthing the neutral. This must be the case at almost all the distribution S/S. Then where does the need for a 11kV (earthed system) come into place? Can you kindly clarify this

Register to Reply
Anonymous Poster
#2

Re: Difference between earthed 11KV cables and unearthed 11KV cables

12/14/2008 11:05 PM

earthed cable is always green and brown from any floor/level/platform/storey of any building less than 100 storeys...... please acknowledge

Register to Reply Off Topic (Score 5)
Participant

Join Date: May 2008
Location: surat, india
Posts: 4
#3

Re: Earthed Cables and Unearthed Cables

12/18/2008 10:03 AM

Hi Mr. Gupta,

What Mr Abraham has said is very true. I am adding few details which I hope may clarify your questions.

(1) For cables to be used in solidly earthed system, the phase-to-armour insulation can be selected for U/root3 volts only. U0= U/root3

(2) If system neutral is resistance-earthed, then the phase-to-ground voltage of the two healthy phases rise up when an earthfault occurs on the third phase. And in healthy two phases the voltage rises to phase to phase value depending on the degree of effectiveness of earthing. Therefore, phase to armour insulation of cables should be U which has been representeted as U/U.

(3) If system is unearthed then as explained in (2) above the U/U will be the insulation level.

(4) IEC standards permit U0/U rating for cables used in high resistance earthed systems if Earth Fault relays clear the fault within 60 seconds - as the cables are tested for 2.2 to 2.8 times U values for 5/10 minutes.

I hope this may help you.

Register to Reply
Anonymous Poster
#5
In reply to #3

Re: Earthed Cables and Unearthed Cables

08/11/2010 1:01 PM

Can you tell which IEC allows U0/U rating for High resistance earthed system

Register to Reply
Anonymous Poster
#4

Re: Earthed Cables and Unearthed Cables

12/21/2008 6:50 AM

dear yogesh,

1) in earthed cables the insulation level provided by the manufacturer between phase ( conductor ) and earth (armour) is 11kv/root3 (ie.phase voltage in 11kv system).

2) in unearthed system the insualtion level provided between phase (conductor) and earth (armour) is 11kv ( ie. line voltage in 11kv sysytem).

3) It is to be noted that insulation level between phase to phase ( conductors ) are 11kv in both earthed & unearthed systems, difference exists only in the insulation level between phase to earth in both systems.

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); dipak desai (1); shivvaram (1); V.I.Abraham (1)