Earth Leakage Trip

12/19/2008 7:05 AM

we are using ELCB 3A rating with 300/3A CT.The connected load are both 3 phases and single phases.The CT primary are all 3 phases and Nuetral.The problem is when CT secondary connected to ELCB , it trip the breaker even all 3 phases load are diconnected.Can you anybody give solution for the probem.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Nov 2008
Posts: 23
#1

Re: Earth Leakage Trip

12/20/2008 3:36 AM

It means there is circulating current in the neutral. This will happen when generators are running in parallel & in stead of one,more than one neutrals are connected to earth. Or otherwise the neutral grounding may not be proper.

Register to Reply
Active Contributor

Join Date: Oct 2006
Posts: 17
#2
In reply to #1

Re: Earth Leakage Trip

12/20/2008 6:35 AM

Thank you, we solved the problem.one of the outgoing feeder cable neutral shorted with ground,Some other circuit current flow to the neutral to ground.After correct the neutral of the feeder, no Earth leakage trip.Thanks for your idea.

Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#3
In reply to #2

Re: Earth Leakage Trip

12/30/2008 6:23 AM

I will suggest to check setting of ELCB, if its low say 20mA it will trip due to very low leakage or circulating current. It could be 50mA or as per local By-law.

Thanks

__________________