Advantages of using a CT having 1A Secondary

12/20/2008 2:08 AM

Dear All, Can anyone of you explain me about the advantages of using a CT having 1A Secondary instead of 5A Secondary. Thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Advantages of using a CT having 1A Secondary

12/20/2008 2:15 AM

Dear Sir,

Normally for MV,EHV (11 and above) CT secondary current is 1 A and and for LV (below 11 kV) CTs are chosen for Secondary Current 5 A is used. All the Protectioncircuits are designed for these rating only.

Best Regards,

N.Suresh

Register to Reply
Participant

Join Date: May 2008
Location: surat, india
Posts: 4
#2

Re: Advantages of using a CT having 1A Secondary

12/20/2008 8:09 AM

Hello lightning.arrester,

The main advantage in selecting the CT of 1A is reducing the ohmic burden which can be seen from following equation.

Rated VA burden = I^2 * rated external ohmic burden where I = rated secondary current.

Since the external ohmic burden remains constant during operation, the CT burden keeps on varying as per the variation in I.

I leave this answer here and ask you to please calculate the Rated burden with I= 1 A and I = 5 A. You will find the main advantage.

Wish you All Merry Christmas & Prosporous 2009.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Oct 2007
Posts: 12
Good Answers: 1
#3
In reply to #2

Re: Advantages of using a CT having 1A Secondary

12/21/2008 11:42 PM

Yes I agree with the reply given by Mr. DD, I would also like to throw some lights in this topics in details.

Secondary Current of CT

The standard CT secondary current ratings are 1A & 5A,The selection is based on the lead burden used for connecting the CT to meters/Relays.5A CT can be used where Current Transformer & protectives device are located within same Switchgear Panel.

1A CT is preferred if CT leads goes out of the Switchgear.

For Example if CT is located in Switch Yard & CT leads have to be taken to relay panels located in control room which can be away.1A CT is preferred to reduce the load burden.For CT with very High lead length,CT with Secondary current rating of 0.5 Amp can be used.

In large Generator Circuits,where primary rated current is of the order of few kilo-amperes only,5A CTs are used, 1A CTs are not preferred since the turns rations becomes very high & CT becomes unwieldy.

thanks

SJ

Register to Reply Score 1 for Good Answer
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); dipak desai (1); SURYAKANT JATANIA (1)

Previous in Forum: question   Next in Forum: Electric Submersible Cable for pumps

Advertisement