polarisation index

12/21/2008 3:31 AM

What is Polarization Index? What is its significance? What is its minimum value?

Register to Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User

Join Date: Oct 2008
Location: Meherrin Virginia
Posts: 319
Good Answers: 6
#1

Re: polarisation index

12/21/2008 10:58 AM

A quick google will tell you that it is the ratio of a 10 minute meggar to a 1 minute meggar test.

There is quite a bit more to it, the usual reason for doing a PI is to prepare for some other test such as suitability for a HiPot (Over Potential) test.

A good PI number can be deceiving, memory tells me that a PI of 2 is acceptable to most OEM' for a new machine, 1.25 to 1.5 for maintenance activities. The problem with those numbers is they don't take into account the actual numbers involved.

You should always perform meggar readings before the PI, if you are looking at a meggar of 10 Ohms then it is obvious you are working with a ground wire instead of a field or stator. the other extreme is if you are getting numbers that indicate a negative PI and the initial resistance value is approaching infinity who really cares what the PI is. This negative PI does happen on occasion.

If you have a bad PI and the numbers seem correct it usually indicates moisture or contamination of some sort.

__________________
If you fail to follow through, you will fail.
Register to Reply
5
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#2

Re: polarisation index

12/21/2008 11:44 AM

What is Polarization Index? What is its significance? What is its minimum value?

Please read this article, its taken from

Copyright Material IEEE Paper No. PCIC-2004-XX

Greg C. Stone IEEE Fellow Iris Power Engineering 1 Westside Drive, Unit 2 Toronto, Ontario M9C 1B2 Canada

II. IEEE 43 – INSULATION RESISTANCE AND POLARIZATION INDEX

IEEE 43 – INSULATION RESISTANCE AND POLARIZATION INDEX

This is probably the most widely used diagnostic test for motor and generator rotor and stator windings. It can be applied to all machines and windings, with the exception of the squirrel cage induction motor rotor winding, which does not have any insulation to test. This test successfully locates pollution and contamination problems in windings. In older insulation systems, the test can also detect thermal deterioration. Insulation resistance (IR) and polarization index (PI) tests have been in use for more than 70 years. Both tests are performed with the same instrument, and are usually done at the same time. The last revision to IEEE 43 was in 1974.

A. Purpose and Theory

The IR test measures the resistance of the electrical insulation between the copper conductors and the core of the stator or the rotor. Ideally this resistance is infinite, since after all, the purpose of the insulation is to block current flow between the copper and the core. In practice, the IR is not infinitely high. Usually, the lower the insulation resistance, the more likely it is that there is a problem with the insulation.

PI is a variation of the IR test. PI is the ratio of the IR measured after voltage has been applied for 10 minutes (R10) to the IR measured after one minute (R1), i.e.:

PI = R10/R1

A low PI indicates that a winding may be contaminated with oil, dirt, insects, etc. or soaked with water. In the test, a relatively high DC voltage is applied between the winding copper and the stator or rotor core (usually via the machine frame). The current flowing in the circuit is then measured.

The insulation resistance (Rt) at time t is then:

Rt = V/It

which is just Ohm's law. V is the applied DC voltage from

the tester, and It is the total current measured after t minutes. The reference to the time of current measurement is needed since the current is usually not constant.

There are four currents that may flow when a DC voltage is applied to the winding. These four are:

1. Capacitive current. When a DC voltage is applied to a capacitor, a high charging current first flows, then decays exponentially. The size of the capacitor and the internal resistance of the voltage supply, typically a few hundred kilohms, sets the current decay rate. A motor stator winding may have a total capacitance of about 100 nF. Thus this current effectively decays to zero in less than 10 seconds. Since this capacitive current contains little diagnostic information, the initial insulation resistance is measured once the capacitive current has decayed. This time before taking the current reading has been set as one minute to ensure that this current does not distort the insulation resistance calculation.

2. Conduction current. This current is due to electrons or ions that migrate across the insulation bulk, between the copper and the core. This is a galvanic current through the groundwall. Such a current can flow if the groundwall has absorbed moisture, which can happen on the older thermoplastic insulation systems, or if a modern insulation has been soaked in water for many days or weeks. This current also flows if there are cracks, cuts or pinholes in the ground insulation (or magnet wire insulation in random wound machines), and some contamination is present to allow current to flow. This current is constant with time, and ideally is zero. With modern insulation, this current usually is zero (as long as there are no cuts, etc) since electrons and ions cannot penetrate through modern epoxy -mica or film insulation. Older asphaltic mica insulations always had non-zero conduction currents, since such insulation systems absorb moisture. If this current is significant, then the winding insulation has a problem.

3. Surface leakage current. This is a constant DC current that flows over the surface of the insulation. It is caused by partly conductive contamination (oil or moisture mixed with dust, dirt, fly ash, chemicals, etc.) on the surface of the windings. Ideally this leakage current is zero. However, if this current is large, it is likely that contamination–induced deterioration (electrical tracking) can occur. This current can be large in round rotor windings where

The polarization index (PI) was developed to make interpretation less sensitive to temperature. PI is a ratio of the IR at two different times. If we assume that R10 and R1 were measured with the winding at the same temperature, which is usually very reasonable to assume, then the 'temperature correction factor' will be the same for both R1 and R10, and will be ratioed out. Thus PI is relatively insensitive to temperature. Furthermore, PI effectively allows us to use the absorption current as a 'yard stick' to see if the leakage and conduction currents are excessive. If these latter currents are much larger than the absorption current, the ratio will be about one. Experience shows that if the PI is about one, then the leakage and conduction currents are large enough that electrical tracking will occur. Conversely, if the leakage and conduction currents are low compared to the absorption current after 1 minute, then PI will be greater than 2, and experience indicates that electrical tracking problems are unlikely. Thus, if we can see the decay in the total current in the interval between 1 minute and 10 minutes, then this decay must be due to the absorption current (since the leakage and conduction currents are constant with time), with the implication that the leakage and conduction currents are minor.

Table 1 Guidelines for dc voltages to be applied during

Winding rated voltage (V) *

Insulation resistance test direct voltage (V)

<100500
1000-2500500-1000
2501-50001000-2500
5001-12 0002500-5000
>12 0005000-10 000

C. Interpretation

What constitutes a 'good reading' and a 'bad reading' depends on the nature of the insulation system and the component (stator or rotor) being tested. Until 2000, the minimum R1 and the acceptable range for PI was essentially the same for all types of stator winding insulation. However, it has been recognized that the modern insulation materials in random wound and form wound stators have essentially no conduction current (as long as there are no cracks or pinholes).

Thus it is possible for a clean, dry, form wound stator winding to have an R1 that is essentially infinite – greater than 100 GW. With an R1 of infinity, calculations of a realistic PI are dubious. Such high R1's are not likely in systems made before the 1970's. Consequently, the maintenance person needs to establish the type of insulation used in the winding, or at least the approximate age of the winding, before interpreting IR and PI results.

Table 2 summarizes how to interpret IR and PI results in stator and rotor windings. The distinction between older and modern insulation systems was set at 1970, although this is somewhat arbitrary. Of note in this table:

1. If R1 is below the indicated minimu m, the implication is that the winding should not be subjected to a hipot test, or be returned to service, since failure may occur. Of course if historical experience indicates that a low R1 is always obtained on a particular winding, then the machine can probably be returned to service with little risk of failure.

2. The minimum R1 is the value corrected to 40oC.

Unfortunately, any more than 10-20oC correction is unlikely to be valid.

3. The minimum acceptable R1 is much lower for old stators than new stators, and it depends on voltage class. For modern stators, the minimum acceptable R1 only depends on whether it is a form wound or random wound stator.

4. For modern form wound stators, if a very high R1 is measured (say greater than 5 GW), then PI is not likely to indicate anything about the winding. Thus, one can save time by aborting the test after the first minute of testing.

5. If the IR or PI is below the minimum in a modern

stator winding, it is only an indication that the winding is contaminated or soaked with water.

6. If a high PI result is obtained on an older stator winding, then there is a possibility the insulation has suffered thermal deterioration. This occurs because thermal deterioration fundamentally changes the nature of the insulation, and thus the absorption currents that flow. The insulation has changed in an asphaltic mica winding if the asphalt has been heated enough to flow out of the groundwall.

Table 2-Recommended minimum insulation resistance values at 400C (all values in MW )

Minimum Insulation Resistance

TEST SPECIMEN

R1 min = kV+1

R1 min = 100

For most windings made before about 1970, all field windings, and others not described below

For most dc armature and ac windings built after about 1970 (form wound coils)

R1 min = 5For most machines with random -wound stator coils and form-wound coils rated below 1kV

In general, the IR and PI tests are an excellent means of finding windings that are contaminated or soaked with moisture. Of course the tests are also good at detecting major flaws where the insulation is cracked or has been cut through. In form wound stators using thermoplastic insulation systems, the tests can also detect thermal deterioration. Unfortunately, there is no evidence that thermal deterioration or problems such as loose coils in the slot, can be found in modern windings

__________________
LOVE FORUM AND DISCUSSION
Register to Reply Good Answer (Score 5)
Commentator

Join Date: Jun 2008
Posts: 80
Good Answers: 5
#3
In reply to #2

Re: polarisation index

12/22/2008 11:30 AM

Nice answer, I gave it a GA. I was working at an east coast power plant years ago and we reinstalled a 6000 HP circulating water pump motor that had been out for maintenance. It had been raining all week and the electricians could not get a good PI. They finally came to our Shift Supervisor and asked if we could start the motor because they were certain the windings were wet and this would solve the bad PI issue. Our Shift Supervisor said no, we would not and sent an operator to look at the motor. The electricians forgot to remove the ground straps from the switchgear. I think everyone on the shift was surprised when the SS said no to the start because it had been raining the whole week. When we heard what the problem was I don't think anyone said a word for about a minute. A line start on a 6000 HP, 4160 VAC motor would have caused extensive damage and anyone in the immediate area would probably have been killed. At an electrical safety conference years later someone had calculated that one megawatt of electric power that arc blasts out of switchgear as a result of a bolted fault is about equal to one stick of dynamite as far as destruction goes. If that is the assumption this would have been like 20 - 30 sticks of dynamite!

Register to Reply
Member

Join Date: Nov 2007
Posts: 7
#4
In reply to #2

Re: polarisation index

07/27/2012 7:28 AM

PI = 600 sec IR value/ 60 sec IR value....Now, if the capacitive current dies out in 60 seconds and conduction current and surface leakage currents are constant, what purpose is served by Meggering beyond 1 minute - after all nothing is going to change in the next 9 minutes? Something missing here?

Register to Reply