Thermal Sensitivity and Turbo Generator

12/21/2008 2:16 PM

Dear Friends

On September 2008, I just finished rewound of GE 237 MVA / 15 kV / 3000 RPM Generator.

Vibration after rewound rotor is normal, and site balancing correction was performed to reduce the vibration, normal standard after rotor has been finished rewound its must be overspeed to made all copper bar rotor setteled, unfortunately its can't to caaried out due to electrical demand, our city need much more electrical power.

Generator has been test by using "thermal sensitivity" method with folowed GE published paper.

Test method:

Step 1 : is to isolate the effects of megawatt loading from VAR loading on the field. Vibration changing as a function of megawatt loading is not a thermal sensitivity mechanism. Megawatt loading may result in rotor vibration excursions as a result of bearing alignment shifts.

Step 2: The first part of the test is to apply constant field current to the field and then to vary the megawatt loading on the generator from 15–60%

The second part of the test is to apply a constant megawatt load to the generator (approximately 60–80%) and then raise field current to maximum rated field current. Each test point should be held until steady state is reached. If the unit is unable to reach maximum field current attainable without a vibration excursion, the series should be repeated but be limited to the maximum field current attainable without exceeding acceptable vibration limits. Again, detailed test data should be taken. A significant change in vibration or phase angle with an increase in field current at constant megawatt load would indicate that the field is thermally sensitive.

This test should then be reversed; that is,decrease field current from its maximum value back down to the starting point. Again monitor all test data. If the vibration and phase angle return to their initial values, then the type of thermal sensitivity can be considered reversible and, in many cases, can be overcome with a compromised balance that moves the thermal vector through zero so that vibration limits are not violated. However, if the vibration levels do not return to the original values and remain high, then this field vibration is considered to be irreversible and corrective actions may involve modification to the field.

If the total vibration of the field stays within acceptable limits, the field is not considered "thermally sensitive." Vibration performance is frequently plotted on a polar chart, because vibration is characterized by amplitude and phase angle. If the vibration vector stays within the 2 or 3 mil circle, or whatever is chosen as an acceptable vibration level, the vibration is not considered to be a problem. This is true even if the phase angle changes and the vibration moves around the interior of this circle.

The change in vibration and phase angle within the polar plot from the starting operating point to the end operating point is called the thermal vector.

Test Result

Bearing 5XBearing 5Y
AmplAngleAmplAngle

30.2

336

18.3

25

60

66

28

228

Thermal vector:

Bearing No. 5X : Vibration thermal vector = 66 micron

Bearing No. 5Y : Vibration thermal vector = 26 micron

Bearing 6XBearing 6Y
AmplAngleAmplAngle

82.2

70

47.3

196

150

79

80

209

Bearing No. 6X : Vibration thermal vector = 62 micron

Bearing No. 6Y : Vibration thermal vector = 49 micron

Based on those test result and refer to the GE standard for thermal vector, the result is still in the safe range or not concider to thermal sensitivity problems.

Questions:

1. what is the vibration cause ?, the highest vib amplitude is 150 micron at bearing no. 6X, alarm setting by customer for this machine is 110, refer to GE manual for this machine is 180 and trip 210 micron.

During test (monitoring by Bently NEvada Instrument), there is not misalignment found.

2. could you advise me what is the problem cause ?

3. its may cause by copper bars rotor has not settled yet in the rotor slot, due to overspeed is not carried out yet ?

Photos documentation.

Rotor finish clean-up & ready to winding re fitting

Rotor winding being in re fitting process

Fault Typical1. cooling duct of turn insulation is not in line with the cooling duct of the copper bar, causing bar to bar short

Fault Typical 2 : inter turn insulation at endwinding has been move out, causing bar to bar short.

Fault Typical3 : Turn insulation breakdown close to cooling duct,

location in the slot portion

Typical fault 4: Hot spot on the turn insulation

Fault Typical 5; Inter turn insulation was loose (unbonded) to copper bar

Low speed balancing when rotor finish rewinding

RSG Inspection after Rotor complete rewound,

RSG was inspected when rotor stand-still (RPM = 0) and

when rotor running without excitation at >0 RPM up to 3000 RPM, no fault indication on the winding during these test.

Following are repair activities taht has been carried-out:

1. NDT on rotor body, steel wedges, bearing shaft, bearings, coupling, etc

2. Degaussing on LP, HP Turbine incl. bearings, casing, etc and rotor generator body, shaft, journal, etc

3. Rotor rewinding using with the old copper bars (all of them has been clean-up)

4. Replace all rotor insulation and upgrade material from class B to class F

5. Low speed balancing by IRD machine

6. Insitu balancing and vibration analyzer by Bently Nevada Instrument

If you have an idea please reply this discussion topic.

Thank you and best regards

Siswanto

__________________
LOVE FORUM AND DISCUSSION
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Oct 2008
Location: Meherrin Virginia
Posts: 319
Good Answers: 6
#1

Re: Experience Sharing "Thermal Sensitivity on Turbo Generator"

12/22/2008 9:50 AM

I wonder as to what your concerns are, regarding the question "what is causing the vibration", You have stated all the reasons that can cause this acceptable vibration.

Is the real question regarding the fact that you did a rewind without a high speed balance and are now concerned that after the coils are thrown out you will see an increase in the thermal sensitivity. I am certain that whoever did the rewind advised you that a low speed balance of a large steam turbine generator field was at best a prudent approach with an uncertain outcome.

I am not at all surprised that you needed a refinement balance shot at speed, I would not have been surprised if you had required a balance shot to even get to speed. I will not be surprised if you need a balance shot to get to overspeed. In the end analysis if you can balance the machine to acceptable limits there is no problem with the balance.

The usual concern with thermal sensitivity is that you cannot apply enough excitation to get full load without exceeding the balance limitations. The usual cause of thermal instability are shorted turns. Who knows whether you will develop the problem when you go to overspeed.

Flux probes will tell the tale, if there is a tale to tell.

Hope I didn't miss your point or insult your intelligence.

__________________
If you fail to follow through, you will fail.
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Experience Sharing "Thermal Sensitivity on Turbo Generator"

12/22/2008 2:24 PM

Dear friend

Thank you for your comment.

Based on GE manual on this machine the vibration is still in acceptance value, but our customer require on their settinglimits.

I have plan to reduce the vibration up to their setting limits by overspeed and after we will correction the balancing by insitu balancing.

Flux probe is not installed on the stator and I can't installed by the temporary flux probe due to the generator is totally enclosed (H2 cooled). But I had test by RSG when generator running without excitation at vary speed, there no anomalies indication was found, the winding is good.

From September until now, the generator has been operated at full MEGAWATT loading but very low MVAR.

May you have experiences to solved our problems to reduce the vibration.

Thank you for your advise....

HAPPY NICE HOLIDAY, HAPPY NEW YEAR 2009

to all our firends

Rgds

Siswanto

Register to Reply
Power-User

Join Date: Oct 2008
Location: Meherrin Virginia
Posts: 319
Good Answers: 6
#3
In reply to #2

Re: Experience Sharing "Thermal Sensitivity on Turbo Generator"

12/22/2008 3:04 PM

Your requirements seem extremely rigid. I hope you and your customer are aware that the best you can do with thermal sensitivity corrections is to reduce it to half the maximum value. The other point is during the balance correction you will find that you can attain this split at only one point in operation. That full value of thermal will raise it's ugly head some place. The one hard fast rule of thermal correction is that you have designate the load or speed that you want the machine to perform with the lowest vibration. This isn't like moving the center of mass to coincide with the center of rotation. It also is not like a critical speed because it doesn't go through it.

I am pretty sure that Bentley Nevada is a wholly owned subsidiary of GE and will have full access to their engineering personnel and database. If you are using this group you would be well advised to continue using them.

__________________
If you fail to follow through, you will fail.
Register to Reply
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#4

Re: Thermal Sensitivity and Turbo Generator

12/23/2008 8:32 AM

Very thank you for your advise,

"HAPPY NEW YEAR 2009 AND HAPPY NICE HOLIDAY"

Rgds

Siswanto

__________________
LOVE FORUM AND DISCUSSION
Register to Reply
Power-User

Join Date: Oct 2008
Location: Meherrin Virginia
Posts: 319
Good Answers: 6
#5

Re: Thermal Sensitivity and Turbo Generator

02/25/2009 10:55 AM

How did this unit run, from the readings? it didn't appear that you were going to have problems.

__________________
If you fail to follow through, you will fail.
Register to Reply
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#6
In reply to #5

Re: Thermal Sensitivity and Turbo Generator

03/04/2009 9:32 AM

Sorry, its too late to reply, due to I just finished our site works to repair exciter rotor GE 35 MW in Malaysia.

Yeah.. the generator running well but only 80% load due to HRG supply limitation, the vibration still remain 150 micron, GE max limit for alarm is 150 um and trip is 228um.. thank you for your attaention to this topic

my regards

siswanto

__________________
LOVE FORUM AND DISCUSSION
Register to Reply
Participant

Join Date: Apr 2012
Posts: 1
#7

Re: Thermal Sensitivity and Turbo Generator

04/03/2012 4:40 AM

Dear Siswanto,

I know it was 4 years ago but i would greatly appreciate if you could tell me what finnally happened. Did you reduce vibrations? what was the problem?. I presently have the same problem in a 324h GE machine and could be very usefull your help.

Thank you veru much in advance.

Register to Reply
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#8
In reply to #7

Re: Thermal Sensitivity and Turbo Generator

04/11/2012 2:47 PM

Dear bilyjoe

Yes its was 4 years ago.

The vibration is cause mechanical problems, No Thermal was found since the Thermal Vector is below than 3 mil

The generator was solved with re balancing when the rotor has spin over speed 20%, with keep the maximum allowed vibration limits.

Why, It can happen ?

Rotor was completely rewound, all of components inside the rotor slot was removed completely and the rotor bars insulation were replaced with new one.

When rotor bars were pulled back into the rotor slot, its not exactly straight, when rotor spin at full speed 3000 RPM, the copper bars in the rotor slot will moving to radial and axial direction, this condition cause unsteady the unbalance vector.

After rotor was spin at over speed, all of rotor components will forced out due to centrifugal forced, when generator to be run at nominal speed 3000RPM, all of the rotor components was steady sited on the slot, so, the vibration vector would be stay steady.

After all components steady, its would be easy to correction for balancing at rated speed 3000RPM.

We proposed to our customer to do this, since this is a standard correction for balancing, but they refused due to it was out from the base time schedule, they do 2 years after, and solved already.

__________________
LOVE FORUM AND DISCUSSION