Bushing Earthing Cap in Power Transformer

12/30/2008 8:18 AM

Dear all

HV bushing of power transformer is earthed at bottom of bushing by means of Earthing cap at normal service condition.Before doing tan delta test,that cap is removed(i.e earth is removed) and tested.

if by mistake that bushing is not earthed before charging the transformer,that bushing will be burst after some period of time.My senior told me ,it is due to heavy voltage developed at the bushing.

My doubt is

1) How that heavy voltage will be developed in the bushing?What is the technical point behind it.

2)what is the approximate voltage developed during this condition that causes bursting?

Regards

gova

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#1

Re: Bushing Earthing Cap in Power Transformer

12/30/2008 11:12 AM

Two different types of power factor test taps are generally used; depending upon the bushing rating. For condenser bushings rated 69 kV and below, a simple power factor test tap is used. The tap bushing is connected to the outer foil layer and grounded (earthed) through the grounding cap. With the cap removed the open circuit voltage between the test tap electrode and ground is typically 500 volts rms.

Condenser bushings rated 115 kV and above are usually equipped with larger potential taps for connection to potential devices or other capacitance networks, if desired. They are also equipped with grounding caps for operation without those devices. The open circuit voltage of these devices is typically 5 kV rms.

With the grounding caps removed, both types of taps can be considered the low sides of capacitance voltage dividers; the high side (C1) being the bushing capacitance from the central conductor to the outer foil and the tap capacitance (C2) between that foil and ground.

Register to Reply Good Answer (Score 2)
Commentator
India - Member - New Member

Join Date: Nov 2008
Location: India
Posts: 72
#2
In reply to #1

Re: Bushing Earthing Cap in Power Transformer

12/30/2008 9:12 PM

Hi bluestone

Thank u very much.I got it.

1)what is the type of test tap used in 230KV and 400KV bushings?

2)Is this 5KV enough to burst the bushing or spoil the insulation ?

KInd regards

gova

Register to Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#3
In reply to #2

Re: Bushing Earthing Cap in Power Transformer

12/31/2008 9:19 AM

230 and 400 kV bushings will normally have a potential tap (or capacitance tap). They will typically use small porcelain bushings with a spring-loaded internal contact to the capacitance tap condenser foil layer. They will also probably have a filler hole in the upper surface of the housing, sealed with a removable pipe plug for insertion of insulating compound in the cavity around the bushing when the tap is to be used with a cable connection to a potential device.

This arrangement provides a useful source of potential for operation of instruments, relays and other devices that do not require metered power. Another advantage is that it offers a practically constant voltage ratio and phase relationship to the high voltage transmission system.

Continuous open circuit operation with the grounding cap removed could cause flashover and damage to the outer portion of the tap bushing.

Register to Reply
Commentator
India - Member - New Member

Join Date: Nov 2008
Location: India
Posts: 72
#4
In reply to #3

Re: Bushing Earthing Cap in Power Transformer

01/01/2009 12:27 AM

Hi bluestone

Thank u very much.

And I wishes all our members to have peace and happiest New year 2009.

Kind regards

gova

Register to Reply
Participant

Join Date: May 2020
Posts: 1
#5
In reply to #2

Re: Bushing Earthing Cap in Power Transformer

05/20/2020 12:09 PM

Hi

I could not understand the concept actually.

How does the voltage builds up to burst the bushing ??

Could you please help me to understand?

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#6
In reply to #5

Re: Bushing Earthing Cap in Power Transformer

05/21/2020 9:22 AM

The paper/foil layers in a HV bushing form a capacitor voltage divider that controls the voltage gradient from the center conductor (HV side) to the mounting flange (grounded side). The capacitance tap is connected to one of the last outer capacitor layers, so that the voltage is not much above ground (as mentioned in other posts, up to 5kV).

Those last layers are only used to test the insulation of the bushing by measuring the capacitance, or to provide a known lower voltage ratio from the HV conductor for metering, protection, etc. If not grounded the voltage can rise to levels that could flash over or puncture the capacitor insulation. Damage to any capacitor layer in the bushing puts electrical stress on the other layers due to the change in voltage across the dividers of the layers. See that links below for some diagrams and additional info:

Fundamentals of Condenser Bushings

Testing & Maintenance of HV Bushings

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Bluestone (2); gova1467 (2); Mahadevakumar (1); PeterT (1)

Previous in Forum: NGR caliculations   Next in Forum: Neutral Wire Connection and ELCB Tripping

Advertisement