Earth Fault Relay Indiacation

01/03/2009 5:55 AM

We have 1925KW DC Motor for 6Hi Reversing Cold Rolling Mill Application . we obsearved Earth Fault Indiacation in Control Drive after running of one or two hours. The Insulation of the Motor is excellent( Megger Value 100 Megaohm). the supply cable condition is also good(Megger value 100megaohm). we also replaced the Earth fault indication Relay but of no use.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Earth Fault Relay Indiacation

01/04/2009 6:56 AM

First you must chek the enter part collcter of brushes try to clean, how is working the fan, chake the armature winding and meassure the the phase curent each other,

Reply Off Topic (Score 5)
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#2

Re: Earth Fault Relay Indiacation

01/04/2009 7:57 AM

I do not see how your Megger test could be good if you have an earth fault indication, have you tested the complete circuit not just the motor windings?

Its a large motor and would suspect a temperature problem but even so to take one or two hours seems rather a long time to heat up to fault indication, larger motors have larger amounts of metal expansion, did your tests take place when the fault showed up or cant you stop the process at that time or is the fault staying put till the end of the production run, then you are testing?? does the fault come back on immediately if you if you restart after shutdown??

It has to be a problem iether your motor or EFI system aproach the problem methodicly and eliminate section by section.

__________________
Dont get on to the roundabout if you dont know how to get off
Reply Score 1 for Good Answer