10/27/2006 10:50 AM
am using Allen Bradley Micro logic 1200 PLC. It is dual port PLC. We r sending ASCII code from PC to PLC having string length of 15. I wish to read each digit separately from received 15 digits. As the each digit & its position has meaning. I cannot send the separate data for each digit.
May I hv software solution with details of instructions I should use to read the each data/ digit separately? I am using RSlogix software of AB.
Pl. inform at the earliest.
Dhananjay
Pune
Good Answers: 50
Re: ASCII code reading at PLC
10/27/2006 11:44 PM
Can't your Allen Bradley store each 8-bit digit into a table, then just translate them against another table that has the ASCII set as its offset?
10/28/2006 5:33 AM
I suggest you use AEX - string extract - to isolate each digit in the string, then ACI - string to integer - on each digit. You could do this in a loop, putting the results into successive locations in an integer file.
10/29/2006 4:37 AM
Thanks! I did the same & work out. Hope further I can do that.
Regards
Dhananjay