I am looking to instal a UPS of 60 KVA. I want to know what will be power consumed by UPS itself while delivering at 50% load.
I was told that a 10 wh load will actually consume about 15 wh (1.5 times power) if powered through UPS.
Kindly help me
Pathfinder Tags: ups
Re: UPS power consumption
01/14/2009 6:58 AM
Different UPS manufacturers have different consumption percentages. I recommend researching the more popular manufactures to get an idea of what is best suited for your application
Here's a list of popular makers:
Powerware - by Eaton
MGE - by Schnieder Electric
APC - also by Schnieder Electric
Liebert - by Emerson
GE digital energy
Chloride Power
I have a powerware 9390 that uses anything from 3KW to 7KW depending on the condition of the batteries
Re: Determining UPS Power Consumption
01/15/2009 5:20 AM
Dear Aruna
Check the UPS efficiency at 50% load, from the UPS manufacturer. Accordingly you can find out the input power. Input power = output power/efficiency
Thanks and regards
Ashok Toshniwal, Bangalore, India
01/15/2009 4:34 PM
Hi Aruna,
In that size of ups they are usually about 83-87% efficent and if it has a Harmonic input filter than efficency should exceed 90% at full load. The efficency drops off at lower loads but should be about 70-75%. I believe your 1.5x number is high a more realistic number would be about 1.3x.
01/15/2009 6:06 PM
I agree exactly with bmcneill. Also, you may want to consult PowerVar, Exide & Oneac.