DG Set Rating

01/15/2009 8:53 AM

Are there any derating factors to be considered while sizing the DG set? If the prime rating of DG set is 500 kVA (i.e.400kW), can it be used to cater 400kW load? I have seen people normally consider only 80% loading on DG sets i.e. in requirement of 400 kW back up, 500kW (625 kVA) rating of DG set will be selected. As per my consideration, DG set of 400kW (500kVA) prime rating can be provided for 400 kW requirement of load. Pl. advise.

Register to Reply
Pathfinder Tags: DG set rating
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Nov 2008
Posts: 23
#1

Re: DG Set Rating

01/16/2009 3:59 AM

Dear Mr Bharat,

When a D.G set has been designed for 500 KVA obviously it has to give an out put power of 400 KW at 0.8 pf provided its run in ideal condition of supply of adequate amount of cool air, complete exhaust of the hot air emanated both from the engine as well as the alternator. The D.G set has to run at the designed limits of ambient temperature, humidity and altitude. The engine is water cooled where as the alternator is air cooled. Therefore cool air has to be force blown to the fan side making the exhaust of hot air from the winding completely out such that the generator room temperature is same as if the generator is standstill. This condition is not possible practically. Therefore we take the safety aspect & derate it to 80% of the KVA rating.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Jan 2009
Posts: 2
#3
In reply to #1

Re: DG Set Rating

01/16/2009 10:01 AM

Thank you for your guidance. As far as temperature is concern, there is a temperature rise test in standards and it has to be taken care that the values of this test are within the limits. And normally, in the manual of DG sets, only a 'well ventilated' room to be provided and forced ventilation does not of their demand. As you say, it seems that 80% loading on DG is only a safety aspect otherwise it can be loaded fully upto it's rating as per the prime rating calculations.

Register to Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#2

Re: DG Set Rating

01/16/2009 7:55 AM

Most generator manufacturers provide guidelines for derating their equipment based on use as standby/prime supply, higher power factor, ambient temperature, altitude, etc. Usually the owner/operator manual includes such guidelines in the initial sections of the manual. There is some variation between recommendations of different manufacturers, so it is best to consult the manufacturer directly. I have encountered machines from some lesser known manufacturers with totally inadequate literature, but I do not expect this to be a problem in the 500 kVA range...Start with the manual, or consult directly with the manufacturer.

Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bharat_Prajapati (1); cwarner7_11 (1); SABNAVEES (1)