Hydrostatic Testing, Radiography Test for pipes

01/16/2009 11:59 PM

Hi

I ahve one question need discussion,

Let is say that we have a 120 m 6 " pipe (new one) and this pipe has 18 welding point, the design code is B31.3 and design pressure is 20 kg/cm2.

the hydrostatic test was ok 30 kg/cm2. But the radigraphiy test has 16.6 % of total weld joints has fail.

and for critical operation we need to run this pipe urgently.

So is it possible to run this pipe depending only in Hydrostatic test without X-RAY.

but what we have to do??? for X-RAY we will do it later.

the working pressre is 16 kg/cm2 and the fluid is flammble.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Dec 2008
Posts: 130
Good Answers: 17
#1

Re: Hydrostatic Testing, Radiography Test for pipes

01/17/2009 12:56 AM

Please confirm a couple of things:

  • Which fluid service is your system designated (most likely Normal)? But just in case - Normal Fluid Service, Category M, or Severe Cyclic (it will not be category D because it is flammable).
  • The entire piping system contains 18 welds total, and every weld was examined.
  • The welds that "failed" actually do not meet the requirements of Table 341.3.2, and that by "fail" you are not just stating that defects were found.
  • Can you list the defects/sizes/locations that were found?

Because, depending on these answers take this scenario for instance.

If your system has been designated Normal Fluid Service (with 5% random RT on butt welds) you may be perfectly fine. It is not the intent of ASME B31.3 that the examinatino ensure that the constructed piping system will be free of defects, even ones that are rejectable if found. Nor is it required that welds that are not examined be free of rejectable defects. Instead, the examination work is part of an overall quality assurance procedure. The leak test is used to test the overall system.

Interpretation 5-18 (May 5, 1987) addresses this point:

-----------------------------------------------------------

"Question (2): Assuming the Engineering Design requires fabrication to ANSI/ASME B31.3, requiring the minimum 5% visual examination and random radiography of girth butt welds, what is the minimum weld quality required by the Code for butt welds which have not been individually examined, but were represented by a successful random visual and radiographic examination?"

"Reply (2): The Code accepts such welds subject to leak testing. Note: The Code assumes that the 5% which were required to be examined will be representative of the entire lot, by a guarantee of such is a contractual matter to be specified by the engineering desig./"

---------------------------------------------

If a piping system passes the examination requirements of the Code, it is accepted (complies with the Code) if it passes the leak test. If additional examinations are performed that reveal defects, it is beyond the Code requirements; the system already complied with the Code, and the issues of whether ot repair those defects and who is to pay for the repair is a purely contractual matter. The defect can be left in and the piping system will still comply with the Code. Of course, it would be judicious to at least perform a fitness-for-service evaluation of the defect if it is intended to be left unrepaired.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#3
In reply to #1

Re: Hydrostatic Testing, Radiography Test for pipes

01/17/2009 11:44 PM

As per 31.3 code hydrostatic shall be conducted 1.5 time the design pressure, regarding RT 5% girth is mandatory requirement , however RT percentage always decide by client speciation or based on joint efficiency factor by designer . IF any joint fail in RT , As per B31.3 there is two penalty RT for each repair per welder.

Mkhan

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2

Re: Hydrostatic Testing, Radiography Test for pipes

01/17/2009 1:06 AM

For pipeline you have to pass the code requirements and the high percentage of failure is strictly not acceptable.

More so since you are working with inflammable liquid.

The hydro test will pass in any weld joint quite easily since a small plug on the defect say a pin hole will not allow the fluid to pass through.

However when the line goes in actual operations, there is a possibility of the defects extending till the pipe fails.

This extension of defects may be due to

corrosion

Cyclic stresses (fatigue)

Normal operating Stresses

Stresses created due to supports, bends, overhangs etc and these will not be accounted for when you are working with hydrostatic test.

Both Hydro and RT/UT etc are complementary and in our pipelines where these are handled (Gas Pipes etc) - additional LPI/MPI depending upon the fluid is carried out. Of course these being for customers, we go beyond the statutory codes.

Moral of the story: forbidden even if urgent, repair. One can not play with safety of persionnel/ plant.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru

Join Date: Jul 2006
Location: Silicon Valley
Posts: 5356
Good Answers: 50
#4

Re: Hydrostatic Testing, Radiography Test for pipes

01/18/2009 5:40 AM

Woof!!! The X-Rays don't lie! I hope your pipeline runs no where near people. You don't want to be like the people in Southern California that suddenly heard it raining, but on closer inspection found out that their entire neighborhood was being showered in gasoline from a busted pipe!!!

__________________
"Perplexity is the beginning of dementia" - Professor Coriolus
Register to Reply