powerfactor correction in primerily welding transformer loads

01/17/2009 11:27 PM

I want to correct the foper factor in primerily welding transformer which is constitutes 60 t0 70% of loads and the other loads are motors of various capacities.It could be gross load of 125 KVA. The intelligent PF correction relays do not work properly and often the capacitors fail in such circuits. CAN YOU SUGGEST A PROPER SOLUTION FOR THIS.

Register to Reply
Pathfinder Tags: POWERFACTOR CORRECTION
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Hobbies - DIY Welding - New Member

Join Date: Oct 2008
Location: Cairns, Qld, Australia
Posts: 968
Good Answers: 65
#1

Re: powerfactor correction in primerily welding transformer loads

01/18/2009 6:51 AM

A possibility would be an overexcited synchronous motor whose excitation was tied to the pf of the welding transformer. When load came on the transformer and pf decreased, the excitation of the synchronous motor could be increased to bring pf back to 85% or so.

Don't let it get too close to 100% as this will cause resonance problems.

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#2

Re: power factor correction in primerily welding transformer loads

01/18/2009 11:33 PM

An active harmonics filter of a fast capacitor switch and controller would do it but it won't come cheap. Your installation is probably too small for this type of technology.

The problem with capacitor in welding application are usually caused by resonances since the welder produce a large frequency spectrum that excites all the LCs.

The only cheap solution I can see is to use power resistors in series with your capacitor bank(s) to reduce the bandwidth and damp the resonance. You will probably need about 10% of the bank capacity and use a fan to cool the resistors. This is not energy efficient but should protect the capacitors and the other equipment.

N.B. Don't oversize the capacitor KVAR but use a higher voltage rating. This give you more robust capacitors.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Associate
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2007
Location: India
Posts: 42
Good Answers: 3
#3
In reply to #2

Re: power factor correction in primerily welding transformer loads

01/19/2009 4:21 AM

Dear Sir,

Static Var Compensator(SVC) would have been ideal solution for this problem. But I agree with Mr.Marcot reply , the applcation of dynamic filter like SVC will not be an economic solution in this case.

However as the welding machine produces spectrum of harmonics during operation, and to economise the solution , we may use HP(High Pass )Filter designed for 5 th harmonic.The HP resistor shall be connected in parallel with the reactor.All the frequencies above 5th Harmonics will be filtered ,although not 100% , but sufficient enough without producing any risk parallel resonance with system impedence.

V.Ambarani

__________________
Best Regards
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#4
In reply to #3

Re: power factor correction in primerily welding transformer loads

01/19/2009 8:09 AM

Good, but do not tune at the 5th as the filter could be overwhelmed if a strong source of 5th is in the vicinity. De-tune at 4,3h to 4,5h.

The inductor should conduct most of the 50-60Hz current for power factor correction which is usually the major component. This will reduce the power dissipation in the resistors. This might be a good compromise.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#5

Re: powerfactor correction in primerily welding transformer loads

01/19/2009 8:53 AM

Most transformer style welders if required usually have a fixed bank of PF correction capacitors installed. As the machines are on intermittent use they will have a capacitive load when not in use but this generally is more than compensated for by the factory general inductive load. Also when the work is finished they can be switched off altogether.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply