Anonymous Poster

Ge Fanuc Plc

01/18/2009 10:28 AM

Hi all

I've come to the realization that programming a PLC is a lot like beating my head against the wall. It just feels so good when I stop.

Anyway,if any of you out there in PLC land could help, it sure would be appreciated.

What I've been trying to do is program a Ge Fanuc 90/30 plc to monitor the temperature of my solar water heater to turn the pump on and off at a given temp via a thermocouple.

At 2.6 millivolts I get the desired temp to turn on at 100 degree temp, but I'll be damned if I can figure out what to write for the program for the analog module to see.

Ok, I'm admitting my faults and lack of knowledge on this, and I'm on my knees begging.

Any bleeding heart takers?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Jan 2008
Posts: 33
#1

Re: Ge Fanuc Plc

01/18/2009 12:28 PM

Wish i could help you with specifics but,

I have just purchased a 5 DVD disc set, A Guide to Understanding PLCs @ http://PLCS.net

Regards,

Jim

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Ge Fanuc Plc

01/18/2009 1:16 PM

What is the analog input set up for and where is your signal coming from? AI cards for the 90-30 are either 0-5VDC, 0-10VDC or 4-20ma. 2.6mV is way too low for the average PLC analog input to see, let alone respond to accurately. You will need to amplify it using what is called a "signal converter".

If that 2.6mV is from a thermocouple (TC), you either need a converter that is made specifically for that TC type, i.e. J, K, N, T etc. and convert it to 4-20ma, or you will need to buy a specific TC analog input card. Unfortunately for the 90-30, the TC input cards only come in 4, 6 or 8 channel versions, so they may end up being a lot more expensive than just finding a converter if you already have a 4-20ma AI card.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Anonymous Poster
#3

Re: Ge Fanuc Plc

01/18/2009 3:39 PM

thanx for the replies

I kinda suspicioned the low voltage would be a problem and that an amplifier would be needed. Thanks a lot for verifieing that for me.

I'm thinkin my best bet would be to go with an electronic temp sensor that would read off the thermocouple. And if I ever get all this damned snow removing done, that's what I'll do.

Reply
Guru

Join Date: May 2007
Location: Geelong, Australia
Posts: 1084
Good Answers: 54
#4

Re: Ge Fanuc Plc

01/18/2009 10:49 PM

I'd suggest you purchase a specialised temperature controller instead. RKC is one brand, there are many others. They don't cost much and will simplify everything.

Wire the T/C to the controller and it'll have a built in display, adjustable setpoints, adjustment for various sensor types, broken lead detection and a voltage free output to tell the motor to go.

__________________
If there's something you don't understand...Then a wizard did it. As heard on "The Simpsons".
Reply
Anonymous Poster
#5

Re: Ge Fanuc Plc

01/18/2009 11:17 PM

Another thing you could do is simply use a thermistor-based temperature sensor. You'd want to wire the series circuit like this: Ground, series resistor, temperature sensor, 5V supply. Measure the resistance across the series resistor. If you use an NTC (negative temperature coefficient) sensor like this one:

http://www.rs-autosport.net/catalog/product_info.php?cPath=10&products_id=215

the voltage across the series resistor will go up with temperature. You'll want to choose a resistor with a value that is approximately what the resistance of your temperature sensor will be in the middle of the range of temperatures you'll be measuring, in order to maximize linearity of your voltage measurement. The voltage output by this setup will work very well with your analog input. The resistance vs. temperature curve for this sensor can be found here:

http://www.megamanual.com/v22manual/mwire.htm#clt

(scroll down a bit until you find the table.)

You can set up an Excel spreadsheet to calculate a series resistor voltage vs. temperature curve very easily.

The added benefit of using a sensor like this is that it has 3/8" NPT pipe threads, so you can plumb it right into a tee fitting in your water plumbing, if that's where you want to measure the temperature.

Hope this helps,

-Rodney

Reply
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#6

Re: Ge Fanuc Plc

01/19/2009 10:50 AM

Are you using Proficy ME or LogicMaster90 software?

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson