Anonymous Poster

selection of incoming voltage

01/21/2009 8:24 AM

A very basic question as Iam a starter in the field. What is the selection criteria for the incoming HT voltage level?. Iam being from India, had observed consumers having demand of 4 to 5 MVA & above prefer to have 33KV HT line & below the said demand prefer to have 11KV HT supply line. As for as my understanding, P = V I Cosθ where in required V as in our case = 415 V for 3 Ph system. When 11 KV is sufficient enough to be steped down to 415V, what is the need of 33 KV HT supply?. Is their any direct link between the demand & selection of HT supply voltage level? Or is that only the transmissionlosses influencing the selection. Request the scholars to throw some light on the same. Thanks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Jan 2009
Posts: 1
#1

Re: selection of incoming voltage

01/21/2009 11:51 AM

Well friend!

Selection of Voltage levels of a system depends mainly on the transmission ditance(i.e. the distance between place of power generation & end power user) .

& consequently the voltage drop in the line.

Moreover, Higher the voltage level of the system, lower are the losses in it.,but for very short distances the cost of having such high voltage levels is not justified economically....

So power system designers select an appropiate voltage level of the power distribution system from above mentioned points

Reply Off Topic (Score 4)
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#2

Re: selection of incoming voltage

01/21/2009 12:01 PM

Dear Guest, I invite you to sign up and sign in, so that you may enjoy this forum to the fullest.

You guessed at transmission losses as a factor in the service delivery voltage decision. That is usually a concern of the power authority, not the customer, unless the customer has a great distance to cover beyond his service entry point.

I can tell you that the major factors in this choice relate to cost.

Usually power suppliers charge less at higher voltage delivery values since the customer then supplies and carries the equipment cost, maintenance and losses of transforming down to his service voltage.

Amperage will dictate cable and equipment size, directly affecting cost of those items.

Also you should include the square root of 3 in your formula to accurately determine the amperage of the 3 phase system.

Regards, CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: selection of incoming voltage

01/21/2009 1:46 PM

The really simple answer is that the higher the voltage, the lower the current is needed to produce the same amount of power. Low current means smaller cross sectional diameter cables to carry the current, which means less copper or aluminium in the conductors, which means less cost (as cable cost is proportional to the amount of copper or aluminium included in the cable).

There comes a point in power level where it is cheaper to step-up to a higher voltage transformer, switchgear and cabling to save money due to reduced cabling costs. Cable costs can account for a very large portion of the overall installation cost (especially when long runs of cables are necessary), so moderate savings per meter of cable can add up to big savings really quickly.

__________________
jack of all trades
Reply
Anonymous Poster
#5
In reply to #3

Re: selection of incoming voltage

01/22/2009 2:36 AM

Hi all,

thanks for every one's contribution. As per Jack of all trades, (would have been more convinient if ihad known your real name) more voltage means less current ther by saving in conductor size & equipment. I just have a small hitch here. The secondary side i.e end user side voltage is any how constant i.e 415V. How does that contribute in saving the conductor size. And on the primary side that is on the HT side equipments, there is no flow of current (as for as my little knowledge). again here what contributes the saving? could you please clarrify.

PS: Hi Cjm, sure i will get logged in as a permanent user. thanks for your advise.

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6
In reply to #5

Re: selection of incoming voltage

01/22/2009 2:32 PM

It depends on who you are considering. Put simply, for the lines company transmission at higher voltage means cheaper cables, for large energy usage customers (like large factories, smelters, etc) it is common for them to have their own transformer on site and run high energy usage parts of their plant of high voltage instead of 415V, again to save costs by running cheaper cable. Medium usage customers can also have the lines company transformer moved close to their premises to reduce the length of the 415V cable (hence reducing costs again). As for small energy usage customers such as houses, there is no need to run high voltage (it costs more so there is no benefit).

And on the primary side that is on the HT side equipments, there is no flow of current

There is still a flow of current on the primary side of the transformer even thou the primary and secondary windings are electrically isolated from each other. Have a look on Wikipedia (or some similar site) for a basic explanation on how a transformer works.

As per Jack of all trades, (would have been more convenient if ihad known your real name)

I prefer to stay fairly anonymous, as it is a small country down here and I don't want people to start spamming me on my business email address. The avatar name is far more revealing due to the very broad nature of the engineering work I am, and have been involved in over the years.

__________________
jack of all trades
Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: selection of incoming voltage

01/21/2009 6:38 PM

11 kv is considered a distribution voltage where you have residential and small commercial loads. 4 MVA are usually industrial loads and would load an 11 kv feeder down. You might have a VD problem if the 11 KV feeder was very long. 33 kv is an upper level distribution line or a lower level transmission line and is able to handle larger loads. 33 kv usually will be fed from a larger substation.