Im Aldwin, I want to know how many air changes is desirable in a Manufacturing Plant doing copper tube brazing and welding (30%), Painting (25%), and the rest were assembly area. We are located in KSA.

Thanks.

Aldwin

Register to Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Environmental Engineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: May 2007
Location: Anywhere Emperor Palpatine assigns me
Posts: 2774
Good Answers: 101
#1

Re: Air Changes in Manufacturing Plants

01/28/2009 9:10 PM

That will depend on the Code of Practice in your area. Usually between 20 - 30 air changes per hour is okay, but the best to check with the CoP.

__________________
If only you knew the power of the Dark Side of the Force
Register to Reply
Anonymous Poster
#7
In reply to #1

Re: Air Changes in Manufacturing Plants

08/06/2010 4:50 AM

CR4 Admin: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jul 2006
Location: "Dancing over the abyss."
Posts: 4884
Good Answers: 243
#2

Re: Air Changes in Manufacturing Plants

01/28/2009 11:09 PM

Changes should be higher where you generate fume, it is waste to put entire plant on same (highest needed) schedule, especially if you maintain heat...or airconditioning or maintain other process temperatures in the works. The assembly area needs fewer changes than where you are brazing welding and painting.

This is more critical if materials are leaded, or if the paint is solvent based rather thanpowder coat.

Forgive my ignorance, but what exactly is KSA?

milo

__________________
People say between two opposed opinions the truth lies in the middle. Not at all! Between them lies the problem, what is unseeable,eternally active life, contemplated in repose. Goethe
Register to Reply
Commentator

Join Date: Sep 2008
Posts: 70
#3
In reply to #2

Re: Air Changes in Manufacturing Plants

01/29/2009 1:59 AM

Milo I think he is in Kingdom of Saudi Arabia. Painting 10-20, welding 15-30 and general workplace is 8-10 ACH...

Also check client requirement if any.

Register to Reply
Guru

Join Date: Jul 2006
Location: "Dancing over the abyss."
Posts: 4884
Good Answers: 243
#5
In reply to #3

Re: Air Changes in Manufacturing Plants

01/29/2009 10:32 AM

Ahhhh! Thank you.

milo

__________________
People say between two opposed opinions the truth lies in the middle. Not at all! Between them lies the problem, what is unseeable,eternally active life, contemplated in repose. Goethe
Register to Reply
Anonymous Poster
#4

Re: Air Changes in Manufacturing Plants

01/29/2009 4:05 AM

Instead of looking for ventilation of whole building based on welding/brazing/painting,

please use required localised suction and filter/scrubber units to extract the fumes of these areas and vent out as per environment standards. The building will then be planned for the required /general airchanges ,as specified by government bodies/inspector of factories as applicable. This will be at the minimum level.In many countries it is between 6 to 9 air changes per hour . For operations as mentioned above air change requirements for total building will be much higher if there is no localised extraction.

This will save you money and also take care of enviroment of the manufacturing plants. your workmen will be well protected and will not inhale fumes of such operations. Please also remember unless fresh air is supplied ,extraction devices will not work efficiently.

Register to Reply
Anonymous Poster
#6

Re: Air Changes in Manufacturing Plants

02/19/2009 1:44 AM

Aldwin

For that you need to calculate the area in which the welding, and Painting and assembly going on also look in to Ashrea codes or CIBSE code complies with. And look in to the wind speed the temperature to be maintained in side, SO you have number of parameters need to look through for Ventilation and ACPH

sandeep