Switchyard main bus sizing in one and half breaker scheme

01/31/2009 3:13 AM

Consider following case:

2 x 600 MW three Generator transformer bay

2 station service transformer bay

hooked upto one and half breaker 400 kV switchyard

How the main bus bar is sized in above case?

what is the current rating of individual bay like line bay, transformer bay etc.

Register to Reply
Pathfinder Tags: Switchyard main bus sizing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Jan 2009
Posts: 62
Good Answers: 4
#1

Re: Switchyard main bus sizing in one and half breaker scheme

01/31/2009 5:43 AM

Could you provide the one line diagram for this scheme?

It would greatly help iin the analysis.

__________________
Patriotism is the last refuge of scoundrels
Register to Reply
Anonymous Poster
#8
In reply to #1

Re: Switchyard main bus sizing in one and half breaker scheme

10/08/2009 11:20 AM

main bus one and two shall be 3000amp, bay bus 2000amp.all bay breakers disconnectors 2000amp.this is standard design.

Register to Reply
Member

Join Date: Jan 2009
Location: Baroda
Posts: 7
#2

Re: Switchyard main bus sizing in one and half breaker scheme

02/05/2009 9:25 AM

attached please find the single line diagram for the same.

Register to Reply
Anonymous Poster
#9
In reply to #2

Re: Switchyard main bus sizing in one and half breaker scheme

11/13/2009 6:04 AM

cleaer veiw of single line diagram is required

Register to Reply
Anonymous Poster
#3

Re: Switchyard main bus sizing in one and half breaker scheme

02/10/2009 9:46 AM

Although several other considerations have to be taken into account in sizing the main busses, a simple method is consider total power, take 20% margin on top of that and work out the rating.

In your case, the bus bar may be sized for 3000A.

Short circuit rating needs to be worked out. However, mostly in 400kV system, it works out to be 40kA for 1 sec.

Quad moose conductors or 4" IPS tubes may be selected.

You have to furnish complete details for detailed design.

best wishes

Register to Reply
Member

Join Date: Jan 2009
Location: Baroda
Posts: 7
#5
In reply to #3

Re: Switchyard main bus sizing in one and half breaker scheme

02/12/2009 9:13 AM

I think with the rating of 3000A, I am oversizing my bus bar. Because if we calculate the power flow diagram under different conditions, No section of the bus will see current more than 1200 Amp assuming that each outgoing line can carry upto max of 600 MW (1200 A) of power.

The different conditions, I mentioned above could be

1) when all lines are healthy

2) Outage of any one line or two line simultaneously.

Register to Reply
Anonymous Poster
#7
In reply to #5

Re: Switchyard main bus sizing in one and half breaker scheme

03/08/2009 6:10 AM

Busses must be designed for carrying maximum connected load.

Individual feeders are designed based on expected loads connected.

The rating of 3000Amps is adequate for the busses.

However, you can select single or twin moose or any other conductors for line bays depending upon the maximum current required.

Register to Reply
Commentator

Join Date: Jan 2009
Posts: 62
Good Answers: 4
#4

Re: Switchyard main bus sizing in one and half breaker scheme

02/10/2009 4:57 PM

Our practice in our utility company is to size the main bus bar at full capacity plus 10% (ultimate design). This works out well with our local weather. However, localities of usually higher than 34 deg Celsius temperature may require bigger sized conductors.

Individual bays are sized at their individual full capacities also.

We sometimes overload our systems, but not more than 10% and 1 hour continuously.

__________________
Patriotism is the last refuge of scoundrels
Register to Reply
Member

Join Date: Jan 2009
Location: Baroda
Posts: 7
#6
In reply to #4

Re: Switchyard main bus sizing in one and half breaker scheme

02/12/2009 9:22 AM

Can u kindly calculate the main bus bar and individual bay current rating?

Register to Reply