02/05/2009 8:15 AM

I am replacing two prong outlets with new grounded ones. How would you ground the new outlets that are supplied with two wires?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#1

Re: Outlet Installation

02/05/2009 9:52 AM

By "supplied with two wires", I presume the existing supply wire is #12-2 or #14-2 with no ground.

If the outlet boxes are metal and solidly grounded, the new outlets will be grounded when they are rigidly mounted to the boxes. A short ground wire from the outlet ground terminal to the metal box can also be used. If the boxes are non-metal or ungrounded, a separate ground wire should be installed from the new outlet ground terminal to the nearest system ground. If the boxes are metal and ungrounded, they should be included in the ground connection.

Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#2
In reply to #1

Re: Outlet Installation

02/05/2009 3:44 PM

Bluestone; GA. I believe if you replace them with G.F.I. this is approved. perry

Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#3

Re: Outlet Installation

02/06/2009 12:14 AM

Guest,

Your anonynimity makes answers based on codes very difficult. But, assuming you are in the USA, the National Electrical Code permits replacements to be without a ground if you are in an area where no ground contact is likely. It also permits replacement with a GFI (ground fault interrupter) type of receptacle because a shock hazard to ground would be sensed by the receptacle and power turned-off. If you use a GFI, and put it as the first receptacle in a series, then the rest can be with a ground prong that has no ground connection IF you label each one (labels for this are shipped with the GFI's now). It is best if a ground connection is available, or added. You can connect a separate green or bare grounding wire from the box to the nearest available ground, but this connection is best if it is brought back to the power panel.

Your desire to do this right is commendable. Don't get discouraged if it proves to be time consuming. Many of those older receptacles are downright dangerous because the spring tension to make good contact to a plug is so poor that they can overheat and even cause fires. Be very careful to ensure that the power is off before doing any work, and be prepared to reinsulate wires if the old insulation has become brittle or even started cracking away. Also, be very careful to ensure that the "hot" and "neutral" are on the proper terminals of the replacement receptacle.

--JMM