Could you please write down few words about the differences between Combination Starters and non-Combination Starters?
Thanks,
- MS
Re: difference between Combination Starters and non-Combination Starters
02/05/2009 6:39 PM
A non-combination starter is one that is just the starter and overloads plus control components. A combination starter has a disconnect switch and fuses, enclosed circuit breaker included with the starter and overloads. Does this help you? Let me know.
Joe the Electrical Contractor to the EOR, I know it was suppose to be in my base bid, but I still am going to submit a change order for it.
Good Answers: 244
02/05/2009 7:08 PM
Thanks so much. It helps me lot.
Good Answers: 804
02/06/2009 10:43 AM
It's a little more basic that that, but he has the concept correct.
Every motor control circuit has to have at least the following 3 elements:
  1. Control device, be it manual or automatic,
  2. Motor Overload protection, i.e. overload relay OR overload protection built-in to #1
  3. Disconnect device with Short Circuit protection, either as a circuit breaker, Switch and fuses, or Motor Starter Protector (MSP)
By definition, a "Starter" is anything that makes up 1 and 2.
A "Combination Starter" is 1, 2 and 3