Okay, I give up… I see throughout industry different color codes for switches doing the same function. What is the norm? What is the standard?
Re: Switch Function Color Code
02/07/2009 8:14 AM
Check out the national electric code book, if it doesn't give a direct color code then there isn't one. Many companies like to make their own codes as they go and have their in house electricians follow it to keep everything the same. In our facility, inside our motor starter panels, everything 120V is red, even on a coil. I would use black and white but this is their standard.
CARPE CRUSTULORUM!
Good Answers: 62
02/07/2009 11:26 AM
Local rules rule but
If there is a convention it has probably been put together by the SAE - Society of Automotive Engineers. We use a surprising number of thier specs in aviation.
Location: Currently on break at home in Houston, Texas USA
02/08/2009 7:57 AM
I was an avionics technician in the USAF years ago and all the wiring in an aircraft was the same color - White. Instead of color coding, each wire had a unique wire number imprinted on the insulation every 10" or so. This standard prevented me from washing out of tech school because I had a real color perception problem. In my opinion, it was the best standard that I have ever come across and if I were to manufacture electrical systems, this would be a wiring standard that I would use.
Good Answers: 68
02/08/2009 1:17 AM
Hello dkriley:
It all depends on exactly what you refer to. The piece below explains what has been ratifies by the EU to fit in with the Electrical items manufactured in the East. Though these colours, as you will see as you read the details of why they were changed in the first place, for 'fixed' Electrical Installations.
I hope this is what you were talking about? Please get back to me if I can help in anyway, I will try, OK?
There is ten colours used are with ref' to this standard:
BS 6746C (Colour chart for insulation and sheath of electric cables).
These colors are used in the wire & cable industry to meet Electronic Industries Association (EIA) RS359 Munsell Color Standards.
[The 10 colours are Black, Blue, Brown, Green, Grey, Orange, Purple, Red, White and Yellow.]
This is a short piece from a site which I list directly below:
http://www.emsd.gov.hk/emsd/eng/pps/New_Cable_Colour_Code/en/tech2.html
Type of Cables Affected
The above Task Group envisaged that the cable colour change would mainly affect the supply of LV multi-core cables. High-voltage cables (the conductors of which are identified with numerals) will not be affected by the colour change.
For LV single-core single-insulated cables such as wiring cables in conduits, manufacturers will normally keep certain quantities of these cables in 10 standard colours (i.e. the Munsell colour [see Note 2]) in stock. These 10 standard colours will include both the new and the old colours (i.e. the brown/ black/ grey and red/yellow/blue). These colours are also specified in the standard BS 6746C (Colour chart for insulation and sheath of electric cables).
[Note 2: These colors are used in the wire & cable industry to meet Electronic Industries Association (EIA) RS359 Munsell Color Standards. The 10 colours are Black, Blue, Brown, Green, Grey, Orange, Purple, Red, White and Yellow.]
Cable supply evaluation
Impact of Cable Colour Change on the Safety Compliance, Supply and Price of Electric Cables supplied in Hong Kong Evaluation Report
1.
Purpose
The purpose of this report is to evaluate the impact of cable colour change in the U.K. and other European countries on the safety compliance, supply and price of electric cables supplied in Hong Kong.
2.
Background
Electric cables in Hong Kong are identified by a colour code originated from the U.K. However, for the purpose of standardizing technical requirements, the European countries including the U.K. have aligned their cable colours for fixed electrical installations and a set of new colours (i.e. brown/ black/ grey/ blue/ (green-yellow)) was selected. With the endorsement of the Electrical Safety Advisory Committee (ESAC), the "Working Group on the Review of Cable Colour Code in Hong Kong" (Working Group) was established since year 2003 among the electrical trade and the Electrical and Mechanical Services Department (EMSD) to study the impact brought about by this issue and to make recommendation on the future strategy regarding the cable colour code in Hong Kong. This paper is prepared by the Technical Support Task Group (TSTG) under the Working Group.
3.
Source of Cable Supply
A survey on the source of supply of low-voltage (LV) and high-voltage (HV) electric cables [see Note 1] used in Hong Kong was conducted in year 2004. It was revealed that our cables are mainly imported from the Mainland China and overseas countries such as Japan, the U.K. and South Africa. According to the information provided by the Census and Statistics Department, the source of origin and percentage shares of the total cost of HV and LV cables used in Hong Kong in year 2003 are shown in Table 1 below.
LV Cable
HV Cable
Source of Origin
Percentage
Source of Origin
Percentage
U.K.52%Japan53%
Mainland China11%U.K.18%
South Africa6%Thailand15%
Malaysia6%Malaysia4%
Ireland5%France4%
Others20%Others6%
Table 1 – Source of Cable Supply
[Note1: "high voltage" means voltage normally exceeding low voltage;
"low voltage" means voltage normally exceeding extra low voltage but normally not exceeding- (a) between conductors, 1000V root mean square alternating current or 1500V direct current; or (b) between a conductor and earth, 600V root mean square alternating current or 900V direct current;
"extra low voltage" means voltage normally not exceeding- (a) 50V root mean square alternating current; or (b) 120V direct current, between conductors or between a conductor and earth.]
4.
The above Task Group envisaged that the cable colour change would mainly affect the supply of LV multi-core cables. High-voltage cables (the conductors of which are identified with numerals) will not be affected by the colour change. For LV single-core single-insulated cables such as wiring cables in conduits, manufacturers will normally keep certain quantities of these cables in 10 standard colours (i.e. the Munsell colour [see Note 2]) in stock. These 10 standard colours will include both the new and the old colours (i.e. the brown/ black/ grey and red/yellow/blue). These colours are also specified in the standard BS 6746C (Colour chart for insulation and sheath of electric cables).
5.
Safety Compliance and Alignment with Other Standards
LV cables commonly used in Hong Kong can generally be divided into two categories, i.e. cables used in general installations and fire resistant cables used in essential service and fire service installations. There are a number of certification bodies certifying the safety compliance or quality of electric cables in the world. Two certification bodies, that are commonly adopted by the trade in Hong Kong, are the BRE Certification Limited and British Approvals Service for Cables (BASEC) [see Note3]. They have been consulted regarding product certification beyond April 2006 when our current cable colour code in British Standards will become obsolete and be replaced by new colours.
[Note 3: Loss Prevention Certification Board (LPCB) is under the BRE Certification Limited. LPCB is a recognized mark in products used in fire service installations. BASEC is a recognized mark on quality assurance of electric cables. Electric cables bearing the above product certification mark are recognized as having achieved the required quality.]
The standards of BS 6387, BS 6207 or BS EN60702 or equivalent are currently accepted by the Fire Services Department (FSD). Details are shown in the FSD Circular Letter No. 1/2003 entitled "Minimum Fire Resisting Cable Requirements for Fire Service Installation"(see FSD website: www.hkfsd.gov.hk). According to the reply from BRE Certification Limited, the approval and certification to BS 6387 do not include cable colour. Therefore, the change of cable colour will not affect the safety compliance of fire resistant cables on the aspect of fire safety.
On the certification of safety and quality assurance of cables for general use, BASEC has advised that they do not have any technical difficulty in certifying cables which comply with the new standard.
In addition to the safety compliance and quality assurance issues discussed above, we also need to look into whether our cable colours should fully align with those widely-used national and international standards. Our current cable colour code is originated from the U.K. Since the red/ yellow/ blue/ black/ (yellow-green) colour system in relevant British Standards will become obsolete in April 2006, our current colour code will no longer comply with the new British Standards nor the relevant international standards (e.g. IEC and EN). However, the new colour code (i.e. the brown/ black/ grey/ blue/ (green-yellow)) will fully comply with major reference standards including the IEC, EN and BS.
6.
Cable Supply
According to the results of above survey, a substantial percentage of LV electric cables used in Hong Kong are imported from the western countries. Since the U.K. and the major European countries (members of European Committee for Electrotechnical Standardization (CENELEC)) have adopted the new cable colour code, the supply and manufacturing of cables in old colour code will inevitably be affected.
Although our current cable colour code is still being used by other countries such as Singapore and Malaysia, it is expected that as we get closer to April 2006 when the U.K. will require the new colour coded cables in a mandatory manner, some cable manufacturers will switch to manufacture cables in the new colour code and will avoid keeping stock the old colour coded cables not commonly demanded by the market by them. The market for new colour coded cables will substantially increase and manufacturers are likely to opt for producing new colour coded cables only. Therefore, if our cable colour code remains unchanged, contractors in Hong Kong will need to place special orders for certain types of old colour coded cables in the future. According to the trade practice, a minimum order quantity (MOQ) with a longer delivery time is required for manufacturing cables to special orders. It is expected that the effect of MOQ and longer delivery time will eventually affect the project cost and project time in the Hong Kong industry.
7.
Cable Price
The cable industry adopts the mode of batch type volume production. The contractors in Hong Kong may lose flexibility in choosing cable manufacturers for ordering old colour coded cables due to shrinking of the old colour coded cable market. In the short term, different colour codes are still adopted in different countries. We anticipate that under the current market-driven environment, cable manufacturers will still supply old colour coded cables but at a higher price as compared to the new colour coded cables. In the mid to long-term, the situations will worsen in about 1 to 2 years after April 2006 (the date when the use of the new cable colour coded cable will be mandatory in the U.K.) when certain types of old colour coded cables in stocks have been exhausted.
8.
Conclusion
The adoption of new cable colour code will not affect the safety compliance of electric cables. As our current cable colour code does not comply with the current IEC and EN standards, the adoption of the new cable colour code will therefore enable Hong Kong to align its cable colour code with those adopted by the major western countries. As a substantial percentage of electric cables used in Hong Kong are imported from the western countries in which the new cable colour code have been adopted, the use of the new cable colour code will ensure a stable supply of cable to Hong Kong, prevent possible price fluctuation, and avoid a longer delivery time. Such advantages will benefit the trade and industry and will eventually benefit the general public.
October 2005
Take care............And keep in touch please.................................
Good Answers: 59
02/09/2009 5:45 AM
This post is mainly a note for those respondents who gave information on wiring standards that the question was about coding the function of switches. (It's conceivable the question meant wiring, but...)
But I'd also remark that although the most common 'standard usage' I know is green for ON and red for OFF (and particularly for "emergency off"), I've also seen red used for "use only under if qualified" or "use only in defined conditions", which would be (to put it mildly) a confusing mix!
P.S. Although my colour vision is pretty good, I concur with tropicalspeed about a preferring things in black and white, as maintenance conditions can be far from ideal. However, (and partly for that same reason) I differ with him on favouring the use of printed numbers - on small wires these can become extremely difficult to see, which has been known to force early retirement of experienced and highly competent technicians. For wiring, I far would prefer to see this supplemented with a series of rings whose widths and spacings can be independent of wire diameter; and (returning to thread), for switches patterns should reign wherever possible.
02/09/2009 7:35 AM
I have to agree with you, Physicist, that printed wire numbers on wire sizes smaller than say #14 AWG would be difficult to see especially for us guys who are pushing sixty or better. To the best of my recollection, aircraft wiring was all #14 AWG or larger so, the lettering size was never a problem. different size bands? You may be on to something here but I think that the powers that be would turn this into a color coding scheme again, BBROYGBVGW. I suppose the current numbering applications will continue to be the standard for sometime to come. I didn't mean to get off subject.
It would appear the the most common available colors for operators are; WHT, BLK, GRN, RED, YEL, and BLU. I did some searching and could not come up with anything. I work with marine winches on a regular basis and the operators are coded as such: BLK=Winch pump ON, WHT=Winch pump OFF, RED=Level wind to Port (Jog Right), GRN=Level wind to Starboard (Jog Left), BLU=Pay-out, YEL=Retrieve. These are the only push-button operators used on the winches. The rest of the operators are two-position selectors, I.E., Local-Remote, Off-On. I suspect that any standards concerning switch colors is left up to the designer. It would be interesting to hear from others concerning any color schemes they may encounter.
Good Answers: 61
02/09/2009 12:45 PM
To further confuse things, the power industry standard for breaker & switch indication is red for ON/CLOSED (as in, this is live voltage, and it is DANGEROUS), and green for OFF/OPEN (as in, it will probably not kill you).
Good Answers: 68
02/09/2009 3:26 PM
Hello dkriley,
hope you are well...........Can I ask you a question........To clerify the butter, sorry, matter?
Do you refer to 'up/down' toggle switsh. Other switches can can be turned or moved manually. Or perhaps a 'wire' switch you may see on a schematic?
Take care.....................
Good Answers: 18
02/10/2009 10:34 AM
At best you will find standards from switch manufacturers, and these can change to suit the manufacturer because they are not government regulated. The colors are generally just the result of the colors that are available in the multi-conductor cable that can be purchase in bulk at the lowest price.
Below are a few colors that I find to be consistent with Turck brand DC PNP prox switches. One should never assume that colors will always follow any standard, so never hook up a switch unless you can see how it actuates or have a manufacturer's specs in hand.
2-wire: Brown = DC in, Blue = Load
3-wire: Brown = DC+, Blue = DC-, Black = Load
4-wire: Brown = DC+, Blue = DC-, Black = Load, N.O., White or Green = Load, N.C.