4-20 ma

02/08/2009 11:38 PM

hi friends, please if some one can help me:

before on oil drilling rig i can see meters such as rpm meter driven with 0-10v, but now i see rpm meters driven with 4-20ma such as on top drive system.

my question is why its 4-20ma instead of 0-10v? is that used in hazard locations as it will not be short circuit if meter supply wires shorted? and why it is 4-20 not 0-20ma, is that to make the needle of the meter exactly on zero while it supplied with 4ma and even 1ma will move the needle? as when the supply is 0ma it needs 2 or 3, maby 4ma just to generate flux and move the needle?

please advice

many thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#1

Re: 4-20 ma

02/09/2009 1:04 AM

Hi there,

This question has been answered in the instrumentation section.

Briefly - with 0 - 10V or 0 - 20mA your zero is 0. With 4 - 20mA you have an elevated current zero. So 4mA will be your reference point for zero and 20mA will be your reference point for the transmitter span.

The NAMUR standard states that your over current limit is 22mA - indicating a short, and your under current value is 3.6mA which will indicate a wire break. So by having an elevated zero we can now determine a wire break where it would not be possible with 0 - 20mA or 0 - 10V.

There are other calculations that would apply to intrinsic safe areas where your loop inductance and capacitance have to be below certain values.

For further reference visit the NAMUR web site.

Regards,

Craig

Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2

Re: 4-20 ma

02/09/2009 2:07 AM

The electrical instruments systems can transmit the data in various forms (Parallel/Serial/Digital/Analog)

In the Analog form, you have broadly two methods

a) Voltage Signal- where transducer output voltage is proportional to the parameter.

b) Current Signel (Current loop instruments) where the signal, now as per standard HART protocol 4-20 mA, is transmitted, the value a function of the parameter.

The Voltage signal are much easier form but has some accuracy problem.

Due to the long distance between the transducer and the reciever (Voltmeter), even though the current is small, the voltage drop may affect the value as interpreted. Added to that other effects which may affect the resistance of the communication wire may be there.

In the current loop systems, this problem is taken care of, since we here use a current source and not a voltage source.

The current usually is converted to the voltage for digitising/ analog voltage signal at reciever end by putting a small resistor in series and measuring drop across it.

It jhas nothing to do with hazard (the voltage anyway were low) rather with the signal accuracy and also now almost universally the HART

http://www.smar.com/hart.asp

http://www.arcomcontrols.com/products/pcp/Gateways/Hart/AN19960601.pdf

Off topic

Other common protocol is PROFIBUS-DP

www.profibus.com/celummdb/doc/RPA%20UNITED%20KINGDOM/Downloads/CPIC-PROFIBUS%20Introduction.doc.doc

http://www.rtaautomation.com/profibus/

and a few others.

PS: This is a thread for instruments section, there may be more experts in that section.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply
Participant

Join Date: Mar 2014
Posts: 2
#3
In reply to #2

Re: 4-20 ma

03/22/2014 6:36 PM

Hi,

The main advantage of a current signal over a voltage signal is the immunity to disturbance. A current which enters a cable must come out. As long as the cable is intact, no leakage, the current which enters is the current which will exit. A voltage signal may be infuenced from outside the cable. This is the main reason to choose a current signal over a voltage signal. See for some examples "http://www.divize.com/techinfo/currentloop-connection.html"

Another advantage is the live zero (4 mA) which alows to detect wire breakage,

Regards, Heinrich

__________________
Regards
Reply