Can you help me please.. I am testing a 1250 KVA transformer, how many M ohms must be the insulation resistance of this transformer? May you send me a data sheet containing the insulation tests?
The acceptable limits are set by ANSI/IEEE standards for here in the US. I would suggest your getting a copy of these standards. It really varies some for the different transformer types with the various BIL ratings.
__________________
Joe the Electrical Contractor to the EOR, I know it was suppose to be in my base bid, but I still am going to submit a change order for it.
You cannot use standards of different country, you can either obtain datasheet from IEEE(thats international standard as you know) website or find out what is used in your country.
This formula doesn't work for us. For example, in the electric utility where I work, for our 14400/240 kV distribution transformers 500 kVA and below, we have noticed that at 1500 MegOhms, the transformer will not last long (more than 2 years) if installed and energized. At 1000 MegOhms, the transformer will usually fail within the week it is energized. So, we set our minimum insulation at 2000 MegOhms.
In my opinion, if you have no historical records to based on, the limits set by NETA is a more appropriate guide.