Anonymous Poster

how to apply new yahoo

02/12/2009 10:36 AM

dear sir,

if i add capacitor with dg running the pf up to 0.99 PF

what happen in DG set.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: how to apply new yahoo

02/12/2009 8:48 PM

Another homework question?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2
In reply to #1

Re: how to apply new yahoo

02/12/2009 9:05 PM

I don't feel it is, it would have been had he gone to 1.00

a) You put capacitors at load end and not at generator end (you want to compensate the pf of load)

b) Reaching too near 1.00, you may land up in the LC frequency matching the system frequency under some load condition.but if the Real Load (mimic-ing R) is sufficient then i think nothing will happen to the system.

Capacitive load may only have some effect on the stability of system. The current should lag the voltage and this lagging nature is the way the energy is transferred mech to electrical, If the current starts leading, you may convert it into a motor ? Got to think on this aspect. Not sure.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches